Dry fitting Cellular Core ABS

Users who are viewing this thread

Weekend Handyman

Active Member
Messages
437
Reaction score
131
Points
43
Location
Nova Scotia
Hello:

Just wondering. Can I dry-fit cellular core ABS?

I now you can not dry fit solid core PVC or ABS; however, the cellular core stuff seems to seat more deeply when sizing things up.

Thank you :)
 

Tuttles Revenge

In the Trades
Messages
4,189
Reaction score
1,447
Points
113
1.5 and 2 inch are super easy to dry fit. 3 and 4 can be done but you have to make sure your fittings and pipe are super clean and they're difficult to separate.
 

wwhitney

In the Trades
Messages
6,563
Reaction score
1,844
Points
113
Location
Berkeley, CA
I am running 1.5 foam core ABS
Then the nominal socket depth is 11/16", so you can mark 11/16" from the end of your pipe segments to see if your dry-fitting is full depth (or close enough) or not. Equivalently, if you have everything dry fit, you can measure between hubs and add 1-3/8" to check if your pipe segments are full length (or maybe just add 1/16" or an 1/8" less to give yourself a little leeway).

Cheers, Wayne
 

Weekend Handyman

Active Member
Messages
437
Reaction score
131
Points
43
Location
Nova Scotia
Then the nominal socket depth is 11/16", so you can mark 11/16" from the end of your pipe segments to see if your dry-fitting is full depth (or close enough) or not. Equivalently, if you have everything dry fit, you can measure between hubs and add 1-3/8" to check if your pipe segments are full length (or maybe just add 1/16" or an 1/8" less to give yourself a little leeway).

Cheers, Wayne

I will give it a try and let you know the results.
 

Tuttles Revenge

In the Trades
Messages
4,189
Reaction score
1,447
Points
113
I find that most DWV installations don't need to be accurate to the 1/16..

I think that most rough in can be done with tape measures equipped to the "About" degree of accuracy.
 

wwhitney

In the Trades
Messages
6,563
Reaction score
1,844
Points
113
Location
Berkeley, CA
I find that most DWV installations don't need to be accurate to the 1/16..
Sure, but being systematically 1/16" short at each joint can add up and be a problem. Depending on how many fittings are involved.

Now if you dry fit, mark the dry fit insertion depths, find they are all 5/8", and then glue it up without the extra 1/16" of insertion, that's presumably fine, and your result should match your dry fit.

Cheers, Wayne
 
Top