Do main stacks have to be vertical?

Users who are viewing this thread

Arfeller

Member
Messages
88
Reaction score
3
Points
8
Location
Port Angeles, WA
Major remodel. Basically demo'd half the house and rebuilt. Poured a new concrete footing and relocated the bathroom and kitchen. Way more then I first intended. Isn't it always?? But... I messed up and did not allow for a channel through the foundation for the sanitary sewer line.

The sanitary line basically comes right up to the foundation footing with its invert being about the same elevation as the bottom of foundation footing. I would like to bring it up over the footing, through the wood foundation wall and under the house. Keep it horizontal and then tie in the drain lines. I have attached my attempt to draw it out and also a picture of the outside line. There is a little bit of offset I tried to correct with slight twist of the fittings.

I plan to mound up dirt around this to make sure it has protection.

I know I need CO outside the house also, just have not installed until I can confirm I can do this.

Washington state.

plumbingn drawing.gif
main.JPG
 

Reach4

Well-Known Member
Messages
38,858
Reaction score
4,428
Points
113
Location
IL
I think you are asking what the maximum slope for your house sewer line is. Right?

What do you propose -- 1 inch per foot, or what?
 

Arfeller

Member
Messages
88
Reaction score
3
Points
8
Location
Port Angeles, WA
I think you are asking what the maximum slope for your house sewer line is. Right?

What do you propose -- 1 inch per foot, or what?

Thank you for looking at my question and taking time to respond. The normal layouts and alignments I see all have the stack coming in horizontal and then going vertical with the lines inside the house coming into a vertical stack. I was planning on keeping my stack horizontal and coming into the side of it under the house. I should be able to maintain a ~1/8" tp 1/4" per foot slope on the Horizontal after this jog you see in the picture.

After I bring the main line in over the top of the footing I really don't have the elevation to take it vertical and tie in the inside sanitary... At least I don't think I do.
side profile.gif
 

Reach4

Well-Known Member
Messages
38,858
Reaction score
4,428
Points
113
Location
IL
Thank you for looking at my question and taking time to respond. The normal layouts and alignments I see all have the stack coming in horizontal and then going vertical with the lines inside the house coming into a vertical stack. I was planning on keeping my stack horizontal and coming into the side of it under the house. I should be able to maintain a ~1/8" tp 1/4" per foot slope on the Horizontal after this jog you see in the picture.
Not a problem from a performance point of view.

With 1/8 inch per foot, my understanding is that UPC requires local signoff/permisson with 4 inch, and does not allow with 3 inch. Check your local inspector. So if you need 1/8 inch per foot, use 4 inch, and check the local inspectors first.

With IPC code (not relevant to you), I think 1/8 inch per foot is OK, even with as small as 3 inch. and no special permission. I only bring that up because it is functional, but is not allowed in your area.
 

wwhitney

In the Trades
Messages
6,557
Reaction score
1,841
Points
113
Location
Berkeley, CA
The normal layouts and alignments I see all have the stack coming in horizontal and then going vertical with the lines inside the house coming into a vertical stack.
Some terminology from your plumbing code (UPC):

A Stack is a "vertical main" DWV line extending one or more stories

The Building Drain (almost always horizontal) is the lowest level of drains that exit the building, up to the point 2 feet from the exterior of the wall.

The Building Sewer (almost always horizontal) is the exterior drain pipe after the end of the Building Drain

In your drawing, what is the vent you show just to the right of the WC? You need to vent the WC fixture drain before it combines with any other drains. [Except that it can combine with a shower, tub or lavatory if wet venting the WC.]

Cheers, Wayne
 

Tuttles Revenge

In the Trades
Messages
4,176
Reaction score
1,440
Points
113
plumbing drawing.gif
The plan view of your plumbing drawing looks good but needs a minor tweak. Branch a line off for the kitchen from the branch leading to the laundry rather than from the toilet.. Each fixture has its own vent which is missing on the side view, but its there in the plan view. Are you omitting a sink in the bathroom on purpose? You could horizontally wet vent the bathroom too to save a bunch of time and materials . Got a blueprint of the layout that you could post a pic? or draw your walls on your plumbing drawing?
 
Last edited:

Arfeller

Member
Messages
88
Reaction score
3
Points
8
Location
Port Angeles, WA
Ah... Yeah. I see what you are saying about the vent for WC. That change will be easy. Thank you. Layout for walls attached. Also included a sketch that shows the venting configuration. Ignore the drain section as it was an early drawing and did not have the drain lay out correct.

Thank you all for the review and help!

house.gif
bathroom iso.gif
 