Second floor of the house has 4 bedrooms that all see different temperatures. I will list the specs of the bedrooms below. 1st bedroom is currently empty but will likely be a babies room. 2nd and 3rd bedrooms have a 11 and 15 year old and the 4th bedroom is the master. A Nest thermostat for heat only is located in the master. We have a Burnham v84 oil boiler for baseboard heating and hot water that is set to 195°. There are 3 zones (basement, 1st floor, 2nd floor) each with a new Taco 007 pump and Taco 3 zone relay. Each floor has nest thermostat. Hardwood floors throughout the whole house and no carpet.
The kids have been saying that their rooms have been cold so I placed a temperature sensor in each of the 3 bedrooms. After checking each sensor and the master bedroom thermostat numerous times throughout the day for the past 2 weeks, I discovered that the 1st bedroom is always 4° colder then the master. The 2nd and 3rd bedrooms are always 3° colder then the master. This may not seem like a big difference BUT, we leave the thermostat set to 66-67° which is comfortable for all of us during the day and night. 63° to sleep is too cold for the kids.
I pulled the covers off every baseboard. I confirmed the fins are all oriented correctly, straightened any bent fins, vacuumed all the dust/debris, and sprayed the fins with vinegar/water mix to clean them. There are no obstructions or any items blocking the bottoms of the baseboards and all baseboards are fully open. I also confirmed that every baseboard is full of fins from end to end with no bare pipe.
We moved into this house about 3 years ago. Last spring I changed all 3 circulator pumps and installed the 3 zone relay to convert the line voltage system to 24v for the new Nest thermostats. At that time, the basement and 1st floor had old Taco 007 pumps and the 2nd floor (where the bedrooms are located) had a Armstong Astro 230ci 3 speed pump set to speed 2. Now every zone has new Taco 007.
I believe the loop runs like this. Master bedroom to 1st bedroom to 2nd bedroom to 3rd bedroom to hallway bathroom to master bathroom to master closet back to boiler. I took some temp readings with the infrared gun directly between the fins. I was reading roughly 155°-160° in the master bedroom and between 140°-150° in the other bedrooms.
I have read about covering a section of fins with aluminum foil which sounds like an easy fix for the master bedroom. But, if the baseboards are undersized for the other bedrooms then I would like to have that fixed. Especially the 1st bedroom if we plan to have another baby.
Is it possible that the Taco pump is not powerful enough for the 2nd floor? I could swap the Armstrong pump back in and turn the speed up if that would fix the problem.
Any ideas?
1st Bedroom - 111 ft2 / 892 ft3 - 4' of baseboard
2nd Bedroom - 148 ft2 / 1184 ft3 - 8' of baseboard
3rd Bedroom - 156 ft2 / 1251 ft3 - 8' of baseboard
(Master) 4th Bedroom - 275 ft2 / 2200 ft3 - 14' of baseboard
The kids have been saying that their rooms have been cold so I placed a temperature sensor in each of the 3 bedrooms. After checking each sensor and the master bedroom thermostat numerous times throughout the day for the past 2 weeks, I discovered that the 1st bedroom is always 4° colder then the master. The 2nd and 3rd bedrooms are always 3° colder then the master. This may not seem like a big difference BUT, we leave the thermostat set to 66-67° which is comfortable for all of us during the day and night. 63° to sleep is too cold for the kids.
I pulled the covers off every baseboard. I confirmed the fins are all oriented correctly, straightened any bent fins, vacuumed all the dust/debris, and sprayed the fins with vinegar/water mix to clean them. There are no obstructions or any items blocking the bottoms of the baseboards and all baseboards are fully open. I also confirmed that every baseboard is full of fins from end to end with no bare pipe.
We moved into this house about 3 years ago. Last spring I changed all 3 circulator pumps and installed the 3 zone relay to convert the line voltage system to 24v for the new Nest thermostats. At that time, the basement and 1st floor had old Taco 007 pumps and the 2nd floor (where the bedrooms are located) had a Armstong Astro 230ci 3 speed pump set to speed 2. Now every zone has new Taco 007.
I believe the loop runs like this. Master bedroom to 1st bedroom to 2nd bedroom to 3rd bedroom to hallway bathroom to master bathroom to master closet back to boiler. I took some temp readings with the infrared gun directly between the fins. I was reading roughly 155°-160° in the master bedroom and between 140°-150° in the other bedrooms.
I have read about covering a section of fins with aluminum foil which sounds like an easy fix for the master bedroom. But, if the baseboards are undersized for the other bedrooms then I would like to have that fixed. Especially the 1st bedroom if we plan to have another baby.
Is it possible that the Taco pump is not powerful enough for the 2nd floor? I could swap the Armstrong pump back in and turn the speed up if that would fix the problem.
Any ideas?
1st Bedroom - 111 ft2 / 892 ft3 - 4' of baseboard
2nd Bedroom - 148 ft2 / 1184 ft3 - 8' of baseboard
3rd Bedroom - 156 ft2 / 1251 ft3 - 8' of baseboard
(Master) 4th Bedroom - 275 ft2 / 2200 ft3 - 14' of baseboard