Cleanout Placement clarification

Users who are viewing this thread

Namber

New Member
Messages
4
Reaction score
0
Points
1
Location
Spokane, WA
Hi all,

I am designing my DWV for basement bathroom and bar sink/powder room. I'm hoping to apply for permits within the next 2 weeks. We are under 2021 UPC and 2021 IBC.

In the bar sink and powder room area, I am trying to figure out how to place my upper terminal cleanout to keep a clean look. I am hoping for some cleanout placement clarification. 707.4 states "Cleanouts shall be permitted to be omitted on a horizontal drain line less that 5 feet in length unless such line is serving sinks or urinals." 707.9 states "Each cleanout in piping 2 inches (50 mm) or less in size shall be so installed that there is a clearance of not less than 12 inches (457 mm) in front of the cleanout."

I am attaching a rough draft of my drain layout. Red wall is load bearing.

1) Is a lavatory considered a "sink" for this code? Based on Figure 707.4, it appears since my lavatory line is less than 5', it does not require a cleanout?
2) Can my upper terminal cleanout be in the cabinet under my bar sink? (I'm assuming because it is a bar "sink" and not a lavatory, a cleanout is required.)
3) Can I then add a cleanout for the toilet where I vent it? I would prefer this cleanout be in the wall, opening into the mechanical area. Would it be better to have it as a cleanout in the floor instead of the wall? I have space for either.

I am open to other plumbing layouts, I have just been messing with it for too long and wanted to get some feedback before I continue on with my design.

Thanks in advance!
 

Attachments

  • IMG_0324 (1).jpg
    IMG_0324 (1).jpg
    67.3 KB · Views: 50

Breplum

Licensed plumbing contractor
Messages
2,186
Reaction score
915
Points
113
Location
San Francisco Bay Area
1. No c.o. Required
2.yes. Inside cabinet is fine
3.yes, c.o. In wall on back side is fine. Clean out/test tee or wye fitting. Don’t use conventional tees for clean outs
 

Sylvan

Still learning
Messages
2,817
Reaction score
717
Points
113
Location
New York
When water Jetting a kitchen waste line in a multi story building I like to install a "conventional Tee"

The reason being I can jet upstream as well as down stream at the base of the stack or on the accessible horizontal
 