Advice for a replace on a 10 seer York

Users who are viewing this thread

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
They are thinking of settling on a rheem
Condenser Model # RP1636AJ2NA (two stage 16 seer )vs the bosch. They based it on bosch availability for parts and their overall place in the industry right now compared to other established brands.

Why a 3 tonner for a 1 ton cooling load? (= crazy, even if 2-stage) The RP1636AJ2NA is a woefully low-capacity low efficiency piece of crap in heating mode, with a max capacity of only 21,600BTU/hr @ +17F, per the table on page 15 of the manual. That's a heluva lot less than your ~26K+ calculated heat load, and WAY more cooling capacity than your 1 ton calculated cooling load. (The output of a 1.5 ton ducted minisplit with a cold-climate type compressor, or a 2 ton full size air handler version would be comparable to the output of that 3 ton Rheem. Just sayin'...) Who cares if it's a 2 stage if it's undersized for the heat load at max rating, and (probably) more than 2x oversized for the cooling load it it's low rating? Keep shopping.

The Bosch BOVB-36HDN1-M18M / BVA-36WN1-M20 (made by Midea) would at least come close to covering your heat load, and would be able modulate down to something like your 1% cooling load. It would still cycle more than it modulates in cooling mode, but not short cycle. Overall it's a much better fit to your load numbers than the Rheem, but an even smaller higher efficiency version is probably better.

Id love the idea of a mini split but the ductwork system is based on the old 10 seer unit for a 1.5 story ish place the room configuration is also an issue - after looking in the basement whoever did the ductwork did a not so great job ill have to get a couple steel elbows and a flex duct or two, theres like 90 degree short bends on at least 3 of the runs- its turning into a hot mess. i was going to see what toaster they had originally but my list had a 10kw in mind. Time constraints/financing and the weather are likely affecting this decision

It doesn't sound like your ductwork could even handle a 3 ton 2 stage 16 SEER unit. What's the rated cfm (and blower motor type) of the air handler they specified?

The smallest unit that fills the bill will have a lower cfm, generating lower static pressures. I suspect the 3 ton air handler is rated for ~1200 cfm @ 0.8" or 1" w.c., whereas a 2 tonner would be <900 cfm. That may not seem like a huge difference, but it is. Bear in mind that the static pressure rises exponentially (third power) with duct velocity. On a given duct system the static pressure at 1200 cfm is more than twice the static pressure at 900 cfm.
 

potatowolf

Member
Messages
31
Reaction score
0
Points
6
Location
Pennsylvania
I have to keep in mind that when i opened this thread with that intent to put in a minisplit system that can be comparable to or better than a 10 seer single stage york.

I obviously have loads of questions- and I don't question your argument that you put forward. I've read quite a few posts you've put on here, and you've proven your experience with this to be more than formidable.

Static pressure and ductwork is where im going to be lost to some of your responses, so I'll open with that.
The previous unit was rated for 1200 cfm so I went apples to apples with that effectively. Going on this, the entire time I was under the impression that the ductwork was rated for >= 1200 cfm, i did a ballpark figure at the time.

( counting registers and returns and sizing) most are 4x10 )
this is from what i saw ductwise-

2nd fl
(3) 4x10
(1) 2x10
(3) 6x12 return
1st fl
(5) 4x10 duct
(4) 2x10 duct
(3) 6x12 return


the air handler is rated for that cfm within the documentation RH2V3621MTANJA.

As to why they chose that unit/s?

They were quoted between 8 - 11k just for an amana or york replacement- and those were 14 seer.
the 16 seer was 11k for amana ASZ160361L 3 ton heat with ASPT37C14 air handler.

They are clearly stuck in a situation, and this is what is available for them right now in comparison. They were told by a friend in hvac getting control boards for Bosch later on if something fails could be an issue. Is there a parts shortage or something right now for brands like bosch ?(pandemic related?). This is all that I know.

I liked the bosch but in terms of the max COP 5 degrees rating off ashp.neep returned 1.86. There was a situation of availability and finding a reputable place that will deliver. Also they were told getting replacement parts if anything goes wrong (pandemic or otherwise) isn't easy and this was another important factor in making the choice. --

General consensus is they wont get a mini split unless its central(unitary) for the existing ductwork. However in terms of actual efficiency of the unit I'm aware of what the compact ducted are capable of doing, The units availability is also in question. They can't or won't do cassettes due to the rooms configuration ( asymmetrical ) imagine a corkscrew but vertically. I'd like to try to do as minimal surgery to the house as possible (again not mine) considering the budget and time constraints moving forward.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Static pressure and ductwork is where im going to be lost to some of your responses, so I'll open with that.
The previous unit was rated for 1200 cfm so I went apples to apples with that effectively. Going on this, the entire time I was under the impression that the ductwork was rated for >= 1200 cfm, i did a ballpark figure at the time.

Old school air handler systems the target design velocity was often ~600 fpm to go with the smallest/cheapest/easiest duct sizing possible, and often missed that target by a bit, yielding static pressures > 1" w.c. along with lower then specified flow. By the system being ridiculously oversized adequate cooling/heating was still maintained despite the actual air flow being smaller than specified. It usually wasn't considered a problem unless the flow was so low that the cooling coil iced over or the overtemp limit safety switch on the furnace heat exchanger was tripping. The low efficiency split capacitor AC motor drives were capable of handling the abuse without overheating or burning out. Though sub-optimal, such systems continue to work, albeit with excessive duct noise and excessive cycling due to oversizing.

An ECM blower motor while highly efficient and quiet, will burn out when chronically subjected to static pressures north of 0.8" w.c., and for optimal performance & efficiency the target max should really be 0.5" w.c. even for those air handlers capable of handling 0.8" w.c.. As a rule of thumb (as lousy as they are), designing ducts for 400fpm maximum velocity (on both supply & return ducts), and using large deep pleated filters (4-6" media) sized as large or larger than the return plenum will usually deliver the goods. So if your original duct design was done well and running 600 fpm velocity when delivering 1200 cfm @ 1" w.c. static pressures, dropping back to a system & air handler that delivers 900 cfm would deliver duct velocity of 600 fpm x (900cfm/1200 cfm)= 450 fpm. The newer-lower static pressure would run about 1"w.c. x (450^3/600^3) =0.42" w.c., which is perfectly fine.

( counting registers and returns and sizing) most are 4x10 )
this is from what i saw ductwise-

2nd fl
(3) 4x10
(1) 2x10
(3) 6x12 return
1st fl
(5) 4x10 duct
(4) 2x10 duct
(3) 6x12 return

Are you mixing duct sizing with register sizing here? The register size is almost irrelevant, since the register boot is at the end of the duct run, imparting a fairly low additional static pressure (unless very undersized or the register is closed.)

What size are the supply & return plenums at the air handler?

A totally crude first rough cut analysis: If those are duct sizes, on the supply duct side it looks like you have 3 x (4 x 10) + (2 x 10) = 140 square inches of duct cross section to the 2nd floor, and 5 x (4 x 10) + 4 x ( 2 x 10)= 280 square inches to the first floor, which together adds up to 420 square inches, or (/144=) 2.9 square feet. At 1200 cfm that translates to an average velocity of 1200/2.9= 414 fpm, which is totally fine, assuming the runs aren't insanely long with lots of twists, turns, and sharp throated ells, etc.. At 900 cfm that's an average velocity of 310 fpm, which is also just fine.

On the return side you have 3 x (6 x 12) = 216 square inches on the second floor (fine for 140" of supply to that floor) and another 216" of return for the first floor, which is UNDERSIZED for the 280 square inches of supply to that floor. Ideally the returns would run 1.25x - 1.5x the supply, but there is some wiggle room there, as long as the return runs are short. The second floor returns are 1.54x supply, the first floor returns are 0.77x the supply- probably never a disaster, but an imbalance between first & second floors big enough to drive outdoor air infiltration when the air handler is running by pressurizing the first floor, depressurizing the second floor. But if the second floor returns are substantially longer (they might be) it may not be worth changing.


the air handler is rated for that cfm within the documentation RH2V3621MTANJA.

Per the manual the RH2V3621MTANJA has an ECM drive motor (almost always necessary to hit SEER 16 or higher), with 21" x 21" plenum connections, rated 800 cfm - 1600 cfm in that plenum size. At the bottom of the chart on p.8 you'll see that the _3621MT_ will run it's nominal 1200 cfm @ 0.5" w.c., dropping to 1162cfm @ 0.5" w.c. with a strip heater installed (which you will need, efficiency be damned!) While the table still shows numbers north of 1000 cfm even at 1" w.c. notice that the nominal power consumption of the blower is roughly TWICE at 1" w.c. than at even higher flow when the static pressure is only 0.3" w.c. . Even though it's "rated" for that, it's never a good idea to run it anywhere near 1" w.c.- they can and DO burn out and a replacement motor can run over a grand(!), installed.



As to why they chose that unit/s?

They were quoted between 8 - 11k just for an amana or york replacement- and those were 14 seer.
the 16 seer was 11k for amana ASZ160361L 3 ton heat with ASPT37C14 air handler.

They are clearly stuck in a situation, and this is what is available for them right now in comparison. They were told by a friend in hvac getting control boards for Bosch later on if something fails could be an issue. Is there a parts shortage or something right now for brands like bosch ?(pandemic related?). This is all that I know.

I liked the bosch but in terms of the max COP 5 degrees rating off ashp.neep returned 1.86. There was a situation of availability and finding a reputable place that will deliver. Also they were told getting replacement parts if anything goes wrong (pandemic or otherwise) isn't easy and this was another important factor in making the choice. --

General consensus is they wont get a mini split unless its central(unitary) for the existing ductwork. However in terms of actual efficiency of the unit I'm aware of what the compact ducted are capable of doing, The units availability is also in question. They can't or won't do cassettes due to the rooms configuration ( asymmetrical ) imagine a corkscrew but vertically. I'd like to try to do as minimal surgery to the house as possible (again not mine) considering the budget and time constraints moving forward.

Availability is a problem for lots of these systems due to pandemic supply chain issues, but unless you're desperate and need it NOW it's better to wait until something more appropriately sized is available. The Bosch units are manufactured by (and I suspect largely designed by) Midea, which is currently the largest supplier of AC equipment in the world. Whether or not the controls for the Bosch units are unique to Bosch is something worth investigating, but I suspect (like many Midea manufactured units) most sub-assemblies are cross referenced to other designs and nameplates.

All of Carrier's mini-splits are now pretty much standard Midea units, many/most even at the cabinet box level (simply a swapped label to make it a Carrier), and going forward it looks like some of their modulating full sized air handler heat pump units are mostly or fully-Midea inside as well. eg: A 2 ton Carrier / Payne / Bryant / Weathermaker / Midea 38MARBQ24AA3 / 40MBAAQ24XA3 pairing would be a pretty good fit f0r your loads. They are all exactly the same Midea unit underneath, and there may be even other brand labels slapped onto that design through other distribution chains. Per the manual the nominal cfm for that 2 tonner at high speed is 882 cfm @ 0.8" w.c. (pretty close to the numbers I've been throwing around), and depending on the duct & filter particulars it can probably come in under 0.3" without major re-hacking of the ducts. It would need a toaster for the cold-snap extremes, but would run decent efficiency with lots of modulation comfort most of the year.

Something like this would better than ANY 3 tonner, and head & shoulders above that low heating capacity Rheem. The Rheem would be OK if your 99% outside design temps were north of 25F, but that's not where you live.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
For the record, what are the local 1% and 99% outside design temps at which the 12,300 BTY/hr sensible (2,200 BTU/hr latent) and 26,700 BTU/hr heating loads were calculated?
 

potatowolf

Member
Messages
31
Reaction score
0
Points
6
Location
Pennsylvania
Design temps were Scranton Wilkes-Barre winter 7 summer 85.
I needed to re-evaluate the manual J i did on the house, theres a cathedral ceiling (one side only) and open vertical space about the breakfast nook , I had to add them in as two separate spaces initially in the manual j, and it raised the overall HC to 28900 heating and 13500 cooling - 2200 latent. :(
 

potatowolf

Member
Messages
31
Reaction score
0
Points
6
Location
Pennsylvania
An ECM blower motor while highly efficient and quiet, will burn out when chronically subjected to static pressures north of 0.8" w.c., and for optimal performance & efficiency the target max should really be 0.5" w.c. even for those air handlers capable of handling 0.8" w.c.. As a rule of thumb (as lousy as they are), designing ducts for 400fpm maximum velocity (on both supply & return ducts), and using large deep pleated filters (4-6" media) sized as large or larger than the return plenum will usually deliver the goods. So if your original duct design was done well and running 600 fpm velocity when delivering 1200 cfm @ 1" w.c. static pressures, dropping back to a system & air handler that delivers 900 cfm would deliver duct velocity of 600 fpm x (900cfm/1200 cfm)= 450 fpm. The newer-lower static pressure would run about 1"w.c. x (450^3/600^3) =0.42" w.c., which is perfectly fine.

Ok so it sounds like as long as the unit regardless of what gets purchased needs to operate within those conditions due to ductwork restriction.


Are you mixing duct sizing with register sizing here? The register size is almost irrelevant, since the register boot is at the end of the duct run, imparting a fairly low additional static pressure (unless very undersized or the register is closed.)

Yes I was! I just pushed what was part of my notes, figured anything can help at this point.

What size are the supply & return plenums at the air handler?

I'll try to get that information.

A totally crude first rough cut analysis: If those are duct sizes, on the supply duct side it looks like you have 3 x (4 x 10) + (2 x 10) = 140 square inches of duct cross section to the 2nd floor, and 5 x (4 x 10) + 4 x ( 2 x 10)= 280 square inches to the first floor, which together adds up to 420 square inches, or (/144=) 2.9 square feet. At 1200 cfm that translates to an average velocity of 1200/2.9= 414 fpm, which is totally fine, assuming the runs aren't insanely long with lots of twists, turns, and sharp throated ells, etc.. At 900 cfm that's an average velocity of 310 fpm, which is also just fine.

On the return side you have 3 x (6 x 12) = 216 square inches on the second floor (fine for 140" of supply to that floor) and another 216" of return for the first floor, which is UNDERSIZED for the 280 square inches of supply to that floor. Ideally the returns would run 1.25x - 1.5x the supply, but there is some wiggle room there, as long as the return runs are short. The second floor returns are 1.54x supply, the first floor returns are 0.77x the supply- probably never a disaster, but an imbalance between first & second floors big enough to drive outdoor air infiltration when the air handler is running by pressurizing the first floor, depressurizing the second floor. But if the second floor returns are substantially longer (they might be) it may not be worth changing.

One of the returns was blocked off in the first floor but that can be remedied.


Per the manual the RH2V3621MTANJA has an ECM drive motor (almost always necessary to hit SEER 16 or higher), with 21" x 21" plenum connections, rated 800 cfm - 1600 cfm in that plenum size. At the bottom of the chart on p.8 you'll see that the _3621MT_ will run it's nominal 1200 cfm @ 0.5" w.c., dropping to 1162cfm @ 0.5" w.c. with a strip heater installed (which you will need, efficiency be damned!) While the table still shows numbers north of 1000 cfm even at 1" w.c. notice that the nominal power consumption of the blower is roughly TWICE at 1" w.c. than at even higher flow when the static pressure is only 0.3" w.c. . Even though it's "rated" for that, it's never a good idea to run it anywhere near 1" w.c.- they can and DO burn out and a replacement motor can run over a grand(!), installed.

Its a considerable concern right now it seems like regardless of unit. They are also worried that a 2 ton will not effectively operate for the space.


For the record, what are the local 1% and 99% outside design temps at which the 12,300 BTY/hr sensible (2,200 BTU/hr latent) and 26,700 BTU/hr heating loads were calculated?

Availability is a problem for lots of these systems due to pandemic supply chain issues, but unless you're desperate and need it NOW it's better to wait until something more appropriately sized is available. The Bosch units are manufactured by (and I suspect largely designed by) Midea, which is currently the largest supplier of AC equipment in the world. Whether or not the controls for the Bosch units are unique to Bosch is something worth investigating, but I suspect (like many Midea manufactured units) most sub-assemblies are cross referenced to other designs and nameplates.

Honestly they can't wait, they found out their 10 seer lost all r22 charge ( guy did a pressure check and left without a response for about 2 weeks) and all they have is emergency heat.

All of Carrier's mini-splits are now pretty much standard Midea units, many/most even at the cabinet box level (simply a swapped label to make it a Carrier), and going forward it looks like some of their modulating full sized air handler heat pump units are mostly or fully-Midea inside as well. eg: A 2 ton Carrier / Payne / Bryant / Weathermaker / Midea 38MARBQ24AA3 / 40MBAAQ24XA3 pairing would be a pretty good fit f0r your loads. They are all exactly the same Midea unit underneath, and there may be even other brand labels slapped onto that design through other distribution chains. Per the manual the nominal cfm for that 2 tonner at high speed is 882 cfm @ 0.8" w.c. (pretty close to the numbers I've been throwing around), and depending on the duct & filter particulars it can probably come in under 0.3" without major re-hacking of the ducts. It would need a toaster for the cold-snap extremes, but would run decent efficiency with lots of modulation comfort most of the year.

I needed to re-evaluate the manual J i did on the house, theres a cathedral ceiling (one side only) and open vertical space about the breakfast nook , I had to add them in as two separate spaces in the manual j, and it raised the overall HC to 28900 heating and 13500 cooling - 2200 latent. :(

Something like this would better than ANY 3 tonner, and head & shoulders above that low heating capacity Rheem. The Rheem would be OK if your 99% outside design temps were north of 25F, but that's not where you live.

I guess that returns to the question of availability of unit. They had a HVAC connection but that seems to be unavailable at the moment.
For the record, what are the local 1% and 99% outside design temps at which the 12,300 BTY/hr sensible (2,200 BTU/hr latent) and 26,700 BTU/hr heating loads were calculated?
 

potatowolf

Member
Messages
31
Reaction score
0
Points
6
Location
Pennsylvania
some minor updates-
also thanks @Dana for taking the time to write all that stuff down!
Plenum box is a john manville type 475 8' supply 12x22"return 11x26"?! current filter dimension 16 x 24" and a mix of 5" 7" and 1' flex in the basement. three of the flex duct runs are making hard 90 degree turns :(
 

potatowolf

Member
Messages
31
Reaction score
0
Points
6
Location
Pennsylvania
went on a separate search again for mini splits unitary and got these
MITSUBISHI SV-KP36NA or SVZ-KA36NA2
Fujitsu ARU36RGLX indoor Fujitsu AOU36RGLX Outdoor
also noted-

AOUG36LMAS1
MXZ-4C36NAHZ2-U1
MXZ4C36NA
SUZ-KA36NAHZ
Fujitsu ARU36RGLX


I guess a question would be what configurations are available for a slim duct air handler in an existing plenum space? ( they have a traditional upflow air handler space)
 
Last edited:

potatowolf

Member
Messages
31
Reaction score
0
Points
6
Location
Pennsylvania
previous
Carrier Model
40MBDQ36-3 / 38MBRBQ36AA3 comes w heat pan
Fujitsu ARU36RGLX - no heat pan for below 5 degrees :(
AOU36RLXFZH / ARU7RLF


today is- air handler types only ( i like the arrowed currently)
SVZ‐KP36NA & SUZ‐KA36NAHZ
FLEXX36HP230V1AO / FLEXX36HP230V1AH <----
BOVB-36HDN1-M18M, BVA-36WN1-M20 <----
 