  1. TGhost

    I'm stuck on boiler high pressure.

    I'll have to shell out somewhere around $1,400. I'll do the install (licensed pipefitter.) Not a good time for this. Isn't that how it usually works.
  2. TGhost

    I'm stuck on boiler high pressure.

    According to their website it is, but I have to pay 70% of the new one.
  3. TGhost

    I'm stuck on boiler high pressure.

    I I can hear the water moving when no water is on, so I think you nailed it. Good times! Thank you for all your help, brother.
  4. TGhost

    I'm stuck on boiler high pressure.

    I shut these two ball valves off and no rise in psi. Its maintaining. I dont see any leaking though, or is it sucking in air somewhere?
  5. TGhost

    I'm stuck on boiler high pressure.

    I shut off the 1/4 turn supply (top of photo) and the valve after the fill valve. I brought the pressure down to 13 psi and it slowly went right back up to 30psi. I have experience with this stuff (obviously not as much as some of you). I'm stumped. No leaks anywhere that I can see or hear...
  6. TGhost

    I'm stuck on boiler high pressure.

    Thats the way I've had them. Still rises. The supply valve is off too.i can hear water running through the hw storage tank even when the water is not being used.
  7. TGhost

    I'm stuck on boiler high pressure.

    They are both parallel to the pipe.
  8. TGhost

    I'm stuck on boiler high pressure.

    I still have this issue. Somebody?
  9. TGhost

    I'm stuck on boiler high pressure.

    I think I still have issues. Also the expansion tank is at 15psi.
  10. TGhost

    I think I still have issues. I'm 30-40 minutes from nashua. I would love your help.

    I think I still have issues. I'm 30-40 minutes from nashua. I would love your help.
  11. TGhost

    I'm stuck on boiler high pressure.

    No leaks. I think I was being a moron. I do believe you nailed the issue. Man, thank you so much. I truly appreciate it. You are great with all your replies. I was hoping you'd chime in. Thanks again, brother.
  12. TGhost

    I'm stuck on boiler high pressure.

    Ahhh. I just replaced the auto fill valve. I have no leaks. So, the water supply valve feeding the fill valve can/should be turned off? I did have a faulty EP but maybe I made a mistake of leaving the 1/4 turn supply open. What do you think?
  13. TGhost

    I'm stuck on boiler high pressure.

    I have a buderus logano boiler in my home. I do most the repairs myself and have some knowledge. The PRV has been releasing water constantly at a slow intermittent rate. Constant puddle. The PRV was bad, I replace it. Still kept relieving pressure so I figured the expansion tank was bad. I was...