  1. Slomoola

    HVAC compressor circuit breaker trips. Change breaker from 30 to 35 amps safe?

    Adding in 100 degree temps, need larger gauge copper to lessen the voltage drop on the in-rush current. Solar energy the same deal. Several factors need visited to upsize the wire. Cheap insurance over time.
  2. Slomoola

    HVAC compressor circuit breaker trips. Change breaker from 30 to 35 amps safe?

    What I've read about hard starts is you have more available current to turn the compressor over from a dead stop, allegedly, over time, will burn the compressor windings out. Mine with the 5-2-1 hard start sure fires faster and easier "audibly", at my house. Again for the above reason, you...
  3. Slomoola

    Roof duct repair

    Rust converter, primer and good outdoor UV rated house paint. Full gloss if you can find it.
  4. Slomoola

    HVAC compressor circuit breaker trips. Change breaker from 30 to 35 amps safe?

    I do not size the wire for the running ampacity only. Usually double or triple that figure depending on tonnage. Why? Compressor is the largest amp draw in the outdoor unit. She will turn over easier and quieter with a larger ga copper whip. Makes the compressor last longer. Use lamp cord if you...
  5. Slomoola

    HVAC compressor circuit breaker trips. Change breaker from 30 to 35 amps safe?

    That compressor has a 92 amp locked rotor rating. Meaning she pulls 92 amps of in-rush current trying to turn the compressor over from a dead stop. The guy saying go down to 12ga wire should be ignored.
  6. Slomoola

    HVAC compressor circuit breaker trips. Change breaker from 30 to 35 amps safe?

    Seeing 15.4 run load amps on compressor tag. Half of a 30 amp breaker. Something is wrong. Putting a 35 amp breaker in should be your last effort. Fix the problem first before throwing parts at it. Possible leg off the compressor shorting or close to a short.
  7. Slomoola

    HVAC compressor circuit breaker trips. Change breaker from 30 to 35 amps safe?

    Did this just happen OR was it from day one when the system was new?
  8. Slomoola

    HVAC compressor circuit breaker trips. Change breaker from 30 to 35 amps safe?

    KILL or OPEN the disconnect or breaker. Measure for AC voltage present. Kill ALL power. Open up the compressor winding power wires. Look for one of the 3 legs shorting out or low Ohms. Make sure ALL connections are tight. Use an AC clamp amp meter and test the running draw across the three...
  9. Slomoola

    Goodman 2.5 ton compressor starts erratically.

    I recommend those 5-2-1 hard start kits. Dropped my electric bill down around 20 bucks per month on a 5 ton compressor. Helped mine start faster and easier. This is what you REALLY need with your erratic start/no-start ups. That 54 amps is your in-rush current. Could be you need to clean up...
  10. Slomoola

    Goodman 2.5 ton compressor starts erratically.

    Yes, if the windings are shorted or close to a short.
  11. Slomoola

    Condensation from air vents.

    Many a factor for sure. Most houses the return is too small.
  12. Slomoola

    Texas plumbing questions. How to repair plumbing leaks

    Not at my house. Prefer more of a quality repair. Buy what you like.
  13. Slomoola

    Condensation from air vents.

    In humid areas, wise to say install a 4 ton to help pull moisture out.
  14. Slomoola

    Condensation from air vents.

    Also the old blower wheel was probably NEVER cleaned and packed full of dirt. Causing less air flow through the house. Running longer pulling more humidity out. Old refrigerant charge was probably not perfect on the old unit. Many a factor that could cause this. Clogged air filters or people...
  15. Slomoola

    heat warming tape for freezing weather

    How long do they last? Heard 3-5 years. Are these fire hazards ran in the attic?
  16. Slomoola

    heat warming tape for freezing weather

    Anyone use that heat tape to keep the pipes from freezing? Specifically on PEX A pipe? Curious how much heat actually gets into the plastic pipe to do what it is to do? Guessing you tape it down then insulate right? Is it even safe for PEX pipe? Not going to burn into the pipe?
  17. Slomoola

    Advice on sealing PVC pipe passing through basement wall

    Some of these are not UV rated. Read the label before buying.
  18. Slomoola

    Pinhole leak

    Remember copper is king. Best in flow, highest cost and longevity. Copper has a 50 year service life. PEX, all I've seen is a max of 25 years.
  19. Slomoola

    Water supply layout design

    Modern brass is not brass anymore. All the good lead is gone. Yes it adds more of a battle in sweating. More cleaning and such. Use lead free solder and flux for lead free solder. That tinning flux is good for DIY people.
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks