Recent content by mitch22

  1. mitch22

    Navien 240A suddenly not as hot in internal recirculating mode

    It's relatively easy. I think it was just a turn. It took more time to remove the assembly to reach it.
  2. mitch22

    Navien 240A suddenly not as hot in internal recirculating mode

    NPE. I've found the part online. On ours, the valve plunger had pushed through its closed / seated location. Re-assembling it worked, but am replacing it just in case.
  3. mitch22

    Navien 240A suddenly not as hot in internal recirculating mode

    Joe - that was the cause! Thanks so much!
  4. mitch22

    Navien 240A suddenly not as hot in internal recirculating mode

    Works fine with recirculation off, reaches the target temperature. But feels about 20 degrees cooler when I put it in internal recirculating mode. Confirmed the dip switches and valve position. This started a few weeks ago. Cleaned the water filters. Everything else seems to be in working...