From |15| side of the circuit breaker I brought a dedicated refrigerator #14 cable to thexisting wall outlet wired with #12 from |20| side.
(Brought home a fairly new 36" side-by-side refrigerator found athe curb.)
Existing #12 in the outlet continues to the other wall outlets in this "enclosed back porch made into a second kitchen".

(From the duplex outlet I disconnected the #12 . In theoutlet box, I wire-nutted the #12 to #12 continuing to the other outlets.
Legal?

Potential problem. If one turns off either |15|20| the other cable in the same box remains energized.

Wanto tie the |15|20| handles buthey do not movenough to fit the metal <[ ]> between them.
Run a piece of #12 through the handle holes? |=|=|

Thank you.
 

wwhitney

In the Trades
Messages
6,590
Reaction score
1,857
Points
113
Location
Berkeley, CA
Potential problem. If one turns off either |15|20| the other cable in the same box remains energized.
The NEC doesn't consider that a problem. It only requires a common disconnect on the two breakers if both circuits feed the same device on a single yoke, i.e. if you split the tabs on the receptacle, and supplied one half from one circuit and one half from the other.

With one circuit just passing through the box, there's no requirement for a common disconnect. Even if both circuits served separate devices in a box, you wouldn't need a common disconnect.

Cheers, Wayne
 