Looking for input on my DWV for 3 lav's.
Planning on everything being 2 inch cpvc. Assume 1/4 slope for the horizontal drain.
Questions:
1. The 90 elbow will be in a stud wall. Will that work?
2. Do I even need the vent for the double lav?

3lav1.jpg

3lav2.jpg

3lav3.jpg

Thanks,
Amy
 
Close but no cigar! On the 2 closest to the verticle drop you have constructed an s-trap. Review your use of horizintal sani-tees.
 
All the vents must be 42" above the floor before they go horizontal.

The fixture drains must connect to the main with a wye and 45, not the santee shown.
 
OK, let's try this again. SLightly different Design

Horizontal vents will be at least 42" above floor or 6" above flood level of the lav.

Is the 90 Ell in the wall going to be OK?
3lav1.jpg

3lav2.jpg

3lav3.jpg
 
Thanks. That is actually a third lavatory. But I will make all the vents the same height.
 
the 90's will work in this scenario, the drawings look good, only the numbers for pitch, height, minimum, and maximum are left out.:)
 