Question venting sink

I am remodeling a bathroom and I want to move the sink to another wall; opposite the toilet wall. I am wondering about how to vent the drain. Is there a way I can put in an in-line vent that vents in the wall?...or can I vent it out an exterior wall? I am on the second floor of a three flat so I don't have access to the roof for draining. what is the easiest way to do this????

thanks
Reply With Quote
  #2  
Old 03-10-2005, 08:49 PM
hj's Avatar
hj hj is online now
Moderator & Master Plumber
 
Join Date: Aug 2004
Location: Arizona
Posts: 13,469
Default vent

The easiest way and the correct way are not always the same. You have other tenants living above you so you cannot stick it out the wall. Pressure from water draining above your unit could pressurize your trap and make it spit water out at you if you use an AAV.
Reply With Quote
  #3  
Old 03-11-2005, 03:04 PM
lorraine lorraine is offline
DIY Junior Member
 
Join Date: Mar 2005
Posts: 2
Default aav vent

I am still trying to come up with a solution for the vent. I want to do it the right way. Can I use a mechanical vent in the wall for venting? I heard positive things about them. any feedback?
thanks
Reply With Quote
  #4  
Old 03-11-2005, 05:33 PM
Mike Swearingen's Avatar
Mike Swearingen Mike Swearingen is offline
DIY Senior Member
 
Join Date: Jan 2005
Location: On Albemarle Sound In Northeastern NC
Posts: 622
Default

Check with your Building Inspection Department to see if you can use an air admittance valve under the sink per local code.
http://www.studor.com/index.htm
Good luck!
Mike
Reply With Quote
  #5  
Old 03-12-2005, 06:05 AM
hj's Avatar
hj hj is online now
Moderator & Master Plumber
 
Join Date: Aug 2004
Location: Arizona
Posts: 13,469
Default aav

YOu will hear "positive things" about them from the manufacturers and guys who use them in order to avoid doing the job "right". Those of us who work with plumbing on a continual basis know that there are situations where they are about the only solution, but also realize that under certain conditions they are the same as having no vent at all. The original concept behind the AAV was that you would install a vent system and then use the AAV as the final piece of it. In your case a plumber would either design some way to get your vent back to the vent stack, and there is more than one way to do it, or use an AAV as a last resort.
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -7. The time now is 02:37 PM.


all rights reserved, Love Plumbing & Remodel, 1992-2009