Question dwv system for new 2 sink installation

I am taking out a sink and putting in 2 sinks in my bathroom on the opposite wall. Luckily I have a crawl-space below and an attic above.
I bought some good plumbing books, but they don't cover pipe sizes

I would like to know how to run the DWV system The sink drains will be run separately, because there is a set of drawers between the sinks.

I will run the sink drains to a pvc pipe in the wall that will go up to the attic (for venting) and down through the floor for drainage.

1) what size diameter should this pipe be?

2) When I join these two DRAIN pipes together in the crawl space, should they "become" a pipe of bigger diameter? If so, how big? can they join with a "T" or does it need to be more of a "Y" so it flows better?
(I know the rule about 1/4"drop per foot of linear/lateral travel.)

3) In the attic for venting, can I use a "T" here or is a "Y" better? How big should the pipe be that I end up putting out through the roof (It will be the two sink vents combined into one pipe for a vent)?


your help is greatly appreciated
Reply With Quote
  #2  
Old 09-02-2004, 07:04 AM
e-plumber's Avatar
e-plumber e-plumber is offline
DIY Senior Member
 
Join Date: Sep 2004
Location: New York
Posts: 137
Default dwv system for new 2 sink installation

1) what size diameter should this pipe be?
>1-1/2" is adequate for 2 lavatory basins<
2) When I join these two DRAIN pipes together in the crawl space, should they "become" a pipe of bigger diameter? If so, how big? can they join with a "T" or does it need to be more of a "Y" so it flows better?
(I know the rule about 1/4"drop per foot of linear/lateral travel.)
>If the pipe is vertical, a sanitary tee acceptable. If horizontal, you need to use a wye<
3) In the attic for venting, can I use a "T" here or is a "Y" better? How big should the pipe be that I end up putting out through the roof (It will be the two sink vents combined into one pipe for a vent)?
>A sanitary tee is acceptable. The pipe passing through the roof may need to be increased for frost over protection if you're in a cold climate, check the local plumbing code<

e-plumber
Reply With Quote
  #3  
Old 09-03-2004, 06:25 PM
handsrusinkc handsrusinkc is offline
DIY Junior Member
 
Join Date: Aug 2004
Posts: 18
Default you missed a question

when I join the 2 pipes together, each 1 1/2 inch diameter, they will be heading horizontally to a larger drainpipe.

Can I join these two pipes together to make a 1 1/2 inch pipe, or should I upsize to a 2inch pipe for this horizontal run?
Reply With Quote
  #4  
Old 09-04-2004, 08:19 AM
hj's Avatar
hj hj is online now
Moderator & Master Plumber
 
Join Date: Aug 2004
Location: Arizona
Posts: 13,483
Default two sinks

Apparently my previous reply disappeared. The drawer unit is immaterial because the pipe will be in the wall. Install a 2" drain approximately in the center between the two sinks. Insert a cleanout in the vertical pipe underneath a 2 x 1 1/2 x 1 1/2 x 1 1/2 fixture cross and then run 1 1/2" pipes horizontally to each sink with an elbow on the end. Then install a 1 1/2" vent through the roof or to an existing vent.
Reply With Quote
  #5  
Old 09-04-2004, 03:58 PM
e-plumber's Avatar
e-plumber e-plumber is offline
DIY Senior Member
 
Join Date: Sep 2004
Location: New York
Posts: 137
Default Codes Vary

Quote:
Originally Posted by handsrusinkc
when I join the 2 pipes together, each 1 1/2 inch diameter, they will be heading horizontally to a larger drainpipe.

Can I join these two pipes together to make a 1 1/2 inch pipe, or should I upsize to a 2inch pipe for this horizontal run?
I do not disagree with over sizing in a case like this but according to plumbing code in this area, an 1-1/2" drain line for (2) lavatory basins is adequate to pass an inspection with flying colors. Although a 2" drain line will probably not clog up as quickly and to be honest, I would most likely install it this way (2") in my own home.
__________________
e-plumber
Reply With Quote
  #6  
Old 09-06-2004, 08:07 PM
handsrusinkc handsrusinkc is offline
DIY Junior Member
 
Join Date: Aug 2004
Posts: 18
Default hey two sinks

two sinks: I don't think I understand what you are offering here, but...

My setup is that of two sinks with a vanity with drawers between them. I can't just connect the two sinks together under the countertop. This is why I decided to run two separate drains, one from each sink and connect them together in the crawlspace. By the way, I'm installing this in my 50 y.o. house and trying not to tear out too much drywall.

Thanks for the help
Reply With Quote
  #7  
Old 09-06-2004, 08:11 PM
LonnythePlumber's Avatar
LonnythePlumber LonnythePlumber is offline
Plumber, Contractor, Attorney
 
Join Date: Sep 2004
Location: Wichita, Kansas
Posts: 319
Default In the Wall

The drains are in the wall and the outlets stub out into the vanity space. You're not forgetting that you need a vent are you?
Reply With Quote
  #8  
Old 06-14-2007, 04:35 PM
froddan froddan is offline
DIY Member
 
Join Date: Jun 2007
Posts: 52
Default 1.5 or 2 inch DWV required?

I am doing a similar project, and my vertical drain is 1.5, and I would like to connect two sinks to it.
I would connect a cross pipe, but I haven't been able to find one that is 1.5x1.5x1.5x1.5
Only 2x1.5x1.5

Will this still be adequate? Pass an inspection for two lavatory sinks?
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -7. The time now is 06:44 PM.


all rights reserved, Love Plumbing & Remodel, 1992-2009