brosnt1 Member Messages 38 Reaction score 0 Points 6 Aug 16, 2007 #1 Can I use 10-2/W GND romex to run power to a central A/C condenser if I mark the white wire? the unit is 220VAC at about 20 amps. Thanks
Can I use 10-2/W GND romex to run power to a central A/C condenser if I mark the white wire? the unit is 220VAC at about 20 amps. Thanks
JWelectric Electrical Contractor/Instructor Messages 2,608 Reaction score 22 Points 38 Location North Carolina Aug 16, 2007 #2 brosnt1 said: Can I use 10-2/W GND romex to run power to a central A/C condenser if I mark the white wire? the unit is 220VAC at about 20 amps. Thanks Click to expand... Yes . . . .
brosnt1 said: Can I use 10-2/W GND romex to run power to a central A/C condenser if I mark the white wire? the unit is 220VAC at about 20 amps. Thanks Click to expand... Yes . . . .