In these older houses it is often impossible for me to run a skilsaw and and anything else at the same time (dust-collecting vac, halogen work lights, compressor plugged in and happens to kick on while I'm making a cut on the chop saw, etc, etc.) I've made far too many trips to the fuse panel. And virtually every tool I use now has to be connected to a dust-collecting HEPA vac for the lead paint rules.
I have been doing electrical contracting work for over 44 years and have yet to see a saw service installed for the construction of a home that would carry every electrical tool on the market today.
It is not a case of installing a circuit big enough to handle all these tools at one time but it is instead a matter of managing the tools being used at one time.
Any dust collector of any size to control lead dust should always be on its own circuit with no other tool. Should your air compressor be of any size at all it also should be on a circuit of its own and not shared with any other motor load.
A half horse power 120 volt motor for a tool when just running and not cutting will draw ~ 10 amps but lock the motor and it will draw ~ 59 amps. In order to start the motor to turning without any load at all it will for a nanosecond draw 59 amps.
Knowing this and then trying to saw while a dust collector and air compressor is plugged into the same circuit is doing nothing but burning out the motors.
It is not a matter of bigger circuits but a tool management problem. Do the math to see for one self just what motor tools do. Multiply the full load amps by 6 to see what the maximum amp draw of the motor will be. A 1/3 hp motor draws 7.2 FLA (full load amps) a ½ hp draws 9.8, a ¾ hp draws 13.8 and a 1 hp draws 16 amps. You will find they draw a LRA (locked rotor amps) of 43.2, 58.8, 82.8, and 96 amps respectfully. To check my numbers one can reference Tables 430.248 FLA for 120 volt motors and 430.251(A) LRC of the NEC.
Installing a larger circuit just so we can operate two or more of these appliances at one time just means that there is more heat energy available when we have other problems.
Edited to add:
It has also been my experience that shop tools just don’t do very well plugged into a 15 amp circuit. It is illegal to use the general purpose circuit of a home for renovations purposes unless the tool being used if protected by a GFCI device.
I don’t know of the times that I have been called by a remodeler to look at the circuits in someone’s home because the breaker kept tripping during construction. A smart contractor will have a temp service installed for any remodel work instead of trying to use the premises wiring of the home they are working on but alas it continues to be done none the less.
Should you try to use the premises wiring for your tools then learn how to manage the tools being used at one time and the problem will diminish