I have made some clarifications and changes that were made by Terry L. Do this look like what the inspector will be looking for.

Thanks
John
 
You will notice that Mr. Polk does not mention using the combo fitting to connect a horiz. drain to a vert. drain.
A sanitary tee would be more appropriate, and in the case of the vertical vent taking off from the tee, a santee
would be required.
 
That tee for the future is not acceptable. Also, the washer and tub can't both occupy the same 2" stack
 
In Issaquah, you will need 2" on the tub until the vent, then 1.5" for the trap and trap arm.

It would be a good idea to separate the tub from the washer stack for suds control. You really don't want washer suds coming up in the bath tub.

The toilet looks fine now.
The kitchen will need a 2" cleanout accessible in the cabinet below the sink.
 