Toilet vent

REXAMUS

New Member
Messages
20
Reaction score
0
Points
1
Location
North Carolina
Searched but couldn't find my answer. I know(think) a toilet needs a 2" vent but is it acceptable to start the vent out as a 1 1/2" and then increase it to 2"? I have 2x4 framing and didn't want to run the 2" through the wall since it would be a giant hole.
 
Find out what code you are under. I think it's the IPC in which case a vent specifically for a toilet is not required only that there be a vent somewhere in the system. As to starting out small and enlarging the answer is no
 