Sprinkler stuck in Zone 1. Won't turn off.

jad0807

New Member
Messages
3
Reaction score
0
Points
0
Location
Texas
I have a 6 zone system. The valves are spread across the yard, not centralized. When I start the system, zone 1 turns on like normal, however it won't move on to zone 2. So, I turn the water off from the Shut Off valve a the street.

I go back inside and turn the system off at the control box. I go back to the street and turn the water back on. Now water is trickling out of the sprinkler heads in zone 1 with the sprinkler system turned off.

Any suggestions?
 
Last edited:
There may also be a problem with the timer as you wrote this, but it sounds like your main problem is the valve for zone 1 in my opinion, is sticking open.
 
Is it the cellanoid or the diaphragm? Or should I replace both? or the whole valve?
 
A more pressing problem is that if you have to turn off the water at the street, you must NOT have the required backflow preventer, since it would have TWO shutoffs and you could turn off either one to stop the flow from the sprinklers.
 
A more pressing problem is that if you have to turn off the water at the street, you must NOT have the required backflow preventer, since it would have TWO shutoffs and you could turn off either one to stop the flow from the sprinklers.
 