Thermostat is a Filtrete 3m-22 http://www.radiothermostat.com/filtrete/products/3M-22/
System is an all electric heat pump/AC system
Connected wires to thermostat as per: http://www.radiothermostat.com/filtrete/guides/3M-22-Installation-10may10.pdf -Page 15: 5 Wire HEAT PUMP with Auxiliary Heat
Didn't have "B" wire, did connect "O" wire. Switches set to HP, electric - as per page 8 of manual
I'll have to check what model heat pump/ac system I have later tonight.
Airhandler model is Goodman A24-10
Heat Pump is Goodman CPE18-1AB
old tstat was having problems kicking on, but it would kick on by itself when set on auto sometimes. new tstat doesn't ever kick on when set on auto
Wiggled green wire where it connects in the air handler, and "auto" fan mode seems to be working now. I read somewhere the blower had a 4 min count down before turning on again. Maybe I was just impatient before when I was testing it?
If I have problems still, I will return.