DonL
Jack of all trades Master of one
Note that the default "FAN" circ. setting is very low for the blower if in the "low" setting (around 500-600 CFM I think.) I've reset mine to "high." Our 90k units are not in table for this on page 48. Even "high" is not that high--something like 1200 CFM I think I measured. So if this is being used for the blower speed when the 4 ton is running, it could be having trouble freezing up from low air flow. That could be the case if there is some sort of miswiring.
Normally you would want the blower to run at 400 CFM per Ton of cooling, So what you are saying makes sense.
If all the system is a Rheem then the system should shutdown if it did detect a Iced up condition, Or at least increase the blower speed to at least 1600 CFM if it was in a dehumidifier mode and seen the was Icing.
Normally the compressor would also cut back if it decreases the fan speed and dehumidify on low stage.
Sounds like the outside unit does not know what the inside unit is doing.
Could be just a wiring problem between a Rheem and a Carrier, Wiring color code maybe.
Thank You for your info Runs with bison.
Enjoy Your Day.
DonL