Everyone must be bored around here.
No, We are just tired of you the "Unknowing" spewing your lack of wisdom on this subject and determined to rebut the bad advice you consistently spew...
We have tried to educate you on the subject but due to a lack of absorbency your grey matter repels knowledge...
This is a common occurrence in some people in your chosen field. Most continue to educate themselves all through life and become very good in the field. Others blindly decide at some point that they know everything and at that point cease to have any value.
In case you missed the POINT - expansion tanks provide no help with a run-away [tampered with] water heater.
And your ball valve with a relief does?
If you will note at the
product link you provided it states...
"It is for applications that require a means to shut off the water supply to the water heater and for providing protection from excess water pressure caused by thermal expansion."
Your assumption that it provides protection with a runaway water heater is completely out to lunch.
A properly sized T&P Valve will provide that protection. In looking at the specifications for the Watts 100XL T&P Valve you will not the following lines of information that do not appear on the product you recommend...
A.S.M.E Rated*, CSA Listed. Self-closing T&P Relief Valves
for Water Heaters up to 105,000 BTU/Hr.
The combined 2 in 1 T&P relief valve provides the least expensive and proven means for protection against both excessive
temperature and pressure emergency conditions.
Provides fully automatic temperature and pressure relief protection for hot water storage tanks and heaters up to 105,000 BTU/HR.
Each water heater and hot water storage tank shall be
equipped with a CSA and A.S.M.E. Rated* automatic temperature and pressure relief valve to protect the heater from excessive pressure and temperature. The device shall be ANSI Z21.22 certified. The BTU discharge capacity of the device
shall be in excess of the BTU input rating of the heater.
Now I'm not a General Engineering Contractor so I don't profess too have knowledge about digging irrigation ditches, land leveling, installing driveways, and ditch digging... Frankly I don't want that knowledge... I'll bow to your excellence or, hire some undocumented day laborers to do the work...
I'm a plumber! That is my area of expertise...
The engineers at Watts are a slightly different type of engineer than you are...
They have expertise in the safety controls needed on a water heater. So me the plumber having an awareness that you lack have decided that...
I will have a safety device that is CSA and A.S.M.E. Rated, ANSI Z21.22 certified, With a BTU discharge capacity in excess of the BTU input rating of the heater...
Now go dig a ditch or, something....