voltage drop

ugabulldog

Member
Messages
72
Reaction score
1
Points
8
Location
Northeast GA
Voltage drop was calculated for #10 wire and I am very close (right at) to the max run so I think I will need to size down to #8 wire running 390 ft. to well,....wire in well is 240' of #10 wire, is this ok to mix 8 & 10 to compensate for volt drop?
 
Last edited:
Actually having the maximum recommended cable length is a good thing. It makes a natural soft starter. #10 wire will go 630' with a 1 HP motor. It doesn't hurt anything to start with #8, except that it won't give you the soft start like 630' of #10 will do.

"Reduced-voltage starters may not be required if the maximum recommended cable length is used. With maximum recommended cable length there is a 5% voltage drop in the cable at running amps, resulting in about 20% reduction in starting current and about 36% reduction in starting torque compared to having rated voltage at the motor. This may be enough reduction in starting current so that reduced-voltage starters are not required."

Heres the link;
http://www.franklin-electric.com/aim-manual/page-36.aspx
 
I have almost the exact same setup and pump is happy for several years and runs on 239 volts after start up. I may even have a 1.5hp motor on it.

But where is the control box? at the beginning of the run, or at the well head?
 
Actually having the maximum recommended cable length is a good thing. It makes a natural soft starter. #10 wire will go 630' with a 1 HP motor. It doesn't hurt anything to start with #8, except that it won't give you the soft start like 630' of #10 will do.

"Reduced-voltage starters may not be required if the maximum recommended cable length is used. With maximum recommended cable length there is a 5% voltage drop in the cable at running amps, resulting in about 20% reduction in starting current and about 36% reduction in starting torque compared to having rated voltage at the motor. This may be enough reduction in starting current so that reduced-voltage starters are not required."

Heres the link;
http://www.franklin-electric.com/aim-manual/page-36.aspx

That is my problem,...I am a little over 630', by a few feet, so I should go with #8, in fear of burning pump up faster, correct?
 