Does anyone see any thing wrong with this tub/shower rough in?

2" branch, 1 1/2" vent, 2" trap reduced to 1 1/2" to pick up the tub drain.


074a.jpg
In particular can the cleanout be in the 1 1/2" vent line? My (the 2" branch line is 64" thus the clean out) I haven't glued this yet so I can change it if need be.

Thanks for taking a look.

Jason
 
I have an access panel that will be installed in the wall behind. Table 7-6 of the California Plumbing Code has the minimum cleanout size for a 2" line as 1 1/2" i'm just trying to figure out if it can be in the vent line in this configuration.
 
So if I change the Wye to the Sanitee with the cleanout plug to 2" can I continue after that with a 1 1/2" vent after the cleanout?
 
Absolutely. Just glue a 2 x 1 1/2 bushing in the top of the c.o. tee. And you CAN use a "cleanout tee" which has a tapped opening for a plug, instead of that sanitary tee and adapter. If you do use the tee, they make a "spigot female adapter" which inserts into the opening so you do not have to use a short piece of pipe. Either of these two ways would let you turn the tee facing the access opening rather than sideways like you have it now.
 
Last edited:
I'm more concerned about lining up that drain and the lack of an overflow if it is a tub.
 