I purchased a house and moved in about 5 days ago to it. It has an AQ 125-BNQ tankless with an install of June 2001 based on writing on the side of the tank.
I've noticed when I shower, it takes about 30 seconds or so to get the hot water flowing. For about 2 minutes, there's no issue, then suddenly all hot water is lost and the water turns ice cold. No adjusting of the shower nozzle helps. Approxmiately 1 minute later, hot water returns just as suddenly as it was lost, and then there's no issue. No other water is being used in the house at the time.
Any idea what the problem might be? The home inspection showed no issues with plumbing or anything. Just wondering why I completely lose all hot water for about a minute.
There is likely an overtemp condition being sensed when the flow is too slow. This is more prone to happen in the summer months when the incoming water is warmer, and the minimum modulation of the burner is still too much to keep the temp from hitting the designed in scald-safety limits. Some versions had tweakable temperature modulation adjustments, but the details may have varied considrably since the late '80s. IIRC Bosch bought the Aquastar line from E.L.M. at some point in the late '90s, so you may have an E.L.M. version, but the manual for one of the Bosch versions lives here:
http://www.tanklesswaterheatersdirect.com/shop/tanklesswaterheaters/manuals/125FX_manual.pdf Bosch played around with ignition schemes a lot, but the basic unit is still pretty much what it was on earlier versions.
The minimum modulated input to these tend to be about 28-35KBTU/hr in, and 2gpm flows are usually enough to keep it from tripping off. To diagnose if it's a minimum-flow issue, try running the hot out of the bathroom sink at a modest flow (not a trickle) while taking the shower, see if it still happens. Alternatively, run the tap at a very low flow, see if it induces the symptom quicker.
If it's right on the edge, running the shower slightly hotter than you usually do from the GET GO (not after it's already flamed out, in which case it'll need to cool off before re-striking), can be enough to keep it from happening.
The fact that the flame-out only occurs once could be a function of the temp of the incoming water varying. If the service pipe in the ground has a section that goes under an asphalt paved driveway, there may be a 1-2 gallon slug of water that's considerbly warmer than the averge due to the solar heated (in summer) chunk of earth under the pavement. Even on city water and deeply buried pipes I measure variations in the temp of incoming water at my place in a range of more than 5F (and a seasonal shift far higher than that between January & July.)
When I was running an old-skool Aquastar (circa 1993) in my house I'd sometimes have to make seasonal adjustments to keep it happy at the flows we were using it. It's been retired for about a year now, but it was retired-working. It definitely had it's quirks, but wasn't terrible. I wouldn't go back though- we're currently heating hot water with an indirect tank heated by a low-mass space heating boiler, which has no flow issues high OR low, and runs with slightly better efficiency overall.