Well Shuts Off

Geolec

New Member
Messages
3
Reaction score
0
Points
0
Location
North Carolina
Couple of times a week the water just shuts off. Well Breaker does not trip but if I turn the breaker off and back on water starts immediately. Happens using shower or just washing hands. Pressure tank looks like new and the switch is a 9013FSG2. Any thoughts ?
 
Bad Breaker or Outlet

I have seen this in the Past . It is a one of 3 items based on your wiring.

1. Bad Breaker. The tripped breaker spring is faulty and the switch does not trip.

2. Bad Outlet - Depending on the wiring from the panel to the pump, check for a bad Outlet or if there is a GFI, bad GFI.

If a bad GFI find the cause of the Ground fault .


I woud repalce the Breaker first , a small low cost reapir.


Kevin
 
Do you have a pump protector in the circuit? If you do, it may be shutting off the pump. Flipping the breaker off and back on would reset the pump protector.
 
Back
Top