how to protect buried black pipe

Users who are viewing this thread

whoru9999

New Member
Messages
3
Reaction score
0
Points
0
Location
illinois
I have very little experience with gas line piping. I just had a Yellow PE gas line ran to my pool heater by a pool contractor. It terminates near the pool heater with what appears to be a compression fitting that is connected in turn a black steel elbow and a short run of black steel pipe. The compression fitting and elbow are buried undergroung (wrapped in protective tape) and the pipe comes up out of the ground to my heater through a valve.

I would like to extend the run by about 48 inches because I have to move my heater. I would like to remove the elbow, and use a black steel pipe length. I have the protective tape (American Presto Pipe Wrap Tape), and plan on wrapping the pipe and fittings, then coating the whole thing with roofing tar. Should this provide enough protection to last for quite a while?
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
If he were a "legitimate" contractor, he would have used a "transition riser" rather than black pipe. IF I were going to bury a steel gas pipe, I would use galvanized pipe, but still wrap it. The only black pipe allowed to be buried is the type with an epoxy coating, but even that is only slightly better than plain black pipe.
 

billyloon

New Member
Messages
1
Reaction score
0
Points
0
Location
USA
ok

You should be ok for such a short run. Good call on the roofing tar over the tape (make sure you prime it before you use the tape wrap). From about 1930-1960s they used to use coal tar coating on all underground carbon steel natural gas transmission lines. They use a better coating now that is factory-applied, but I have seen some of these old coal tar lines hold up very well. My company still has thousands of miles of the coal tar lines running across the USA.
 

Doherty Plumbing

Journeyman & Gas Fitter
Messages
810
Reaction score
5
Points
0
Location
Penticton, BC
Website
www.facebook.com
I have very little experience with gas line piping. I just had a Yellow PE gas line ran to my pool heater by a pool contractor. It terminates near the pool heater with what appears to be a compression fitting that is connected in turn a black steel elbow and a short run of black steel pipe. The compression fitting and elbow are buried undergroung (wrapped in protective tape) and the pipe comes up out of the ground to my heater through a valve.

I would like to extend the run by about 48 inches because I have to move my heater. I would like to remove the elbow, and use a black steel pipe length. I have the protective tape (American Presto Pipe Wrap Tape), and plan on wrapping the pipe and fittings, then coating the whole thing with roofing tar. Should this provide enough protection to last for quite a while?

Unfortunately tape will not prevent that black steel in the ground from rusting.......
 