It is not that you can not use horizontal venting there is just a limit on how far you can run it. Here is the part of the Illinois plumbing code. The part in bold and underlined is about the horizontal venting. But the whole code is important about vent sizing.
Section 890.1580 Size and Length of Vents
...(snip)...
b) Size of Individual Vents. The diameter of an individual vent shall be at least 1¼ inches or at least ½ the diameter of the drain to which it connects, whichever is greater.
... (snip)...
e) Size of Vent Piping. The size of vent piping shall be determined based upon its length and the total number of drainage fixture units connected thereto as provided in Appendix A: Table K. No more than 20 percent of the maximum developed length as determined from Table K may be installed in the horizontal position. Vent piping serving floor drains shall be installed in such a manner as to minimize horizontal vent distances.