Condensate Pump tie into DWV

Lakee911

I&C Engineer (mostly WWTP)
Messages
1,254
Reaction score
1
Points
38
Location
Columbus, OH
Hi all,
Curious to see what you guys recomend for using DWV for drain for a condensate pump. Is this the correct procedure? Condensate Pump Drain to air gap to P trap to DWV system? Any better ideas? Air gap needed? If Condensate drain (from A/C) has a trap, do I still need the airgap and trap after the pump?

Thx
Jason
 
pump

The pump makes the condensate connection from the AC an indirect connection so it does not need a trap. The pump should have a check valve on its discharge connection, so you can make any type of connection to the DWV that will work.
 