Installing joist header

LiamM

New Member
Messages
54
Reaction score
0
Points
0
Location
Massachusetts
Hi

I installed a joist header that spans 2 joists bays. The tail joist was previously sistered, as was one of the trimmer joists. Because of this, I used doubled headers. However, the other trimmer joist was only a single, and I didn't think to double it up.

Both headers are within 3' of the joist support, and the header is less then 6' long, so I could've used a single header/trimmer.

So my question is - I used joist hangers for every connection (tail-header, header-trimmer), along with 16d nails. They stick out past the single trimmer. Is this ok? I could see it either way...the situation only called for singles everywhere, so I should be fine even though I made the header stronger than necessary, OR since I used a doubled header, I should've used a doubled trimmer.

Thanks
 
You lost me with joist headers, tail joists, trimmer joists and single header/trimmer.

Are you making up new words?
Look at UBC 2320.8.4, IRC R502.10, or IBC 2308.8.3. All have similar language. The IRC seems the most conservative by specifically saying a single header. See R502.10 on this link http://www.cbs.state.or.us/bcd/boards/rsb/boardpack/07/100307/public_hearing/ch_05.pdf

Single trimmer joists may be used to carry a single header joist that is located within 3 feet (914 mm) of the trimmer joist bearing. When the header joist span exceeds 4 feet (1219 mm), the trimmer joists and the header joist shall be doubled and of sufficient cross section to support the floor joists framing into the header.
 
Last edited:
Hi Phil, thanks for posting the links.

I was off on the length of the header before a doubled-up one is necessary, but mine is only about 30" long, so a single still would've been fine.

Any thoughts on my situation, whether to just leave as is?

Thanks again
 
Some joist hangers require their own nails -- regular nails will not meet their standards for warranty, code compliance, etc.
 