O orbea1 New Member Messages 10 Reaction score 0 Points 0 Jan 23, 2008 #1 Looking for input on my DWV for 3 lav's. Planning on everything being 2 inch cpvc. Assume 1/4 slope for the horizontal drain. Questions: 1. The 90 elbow will be in a stud wall. Will that work? 2. Do I even need the vent for the double lav? Thanks, Amy
Looking for input on my DWV for 3 lav's. Planning on everything being 2 inch cpvc. Assume 1/4 slope for the horizontal drain. Questions: 1. The 90 elbow will be in a stud wall. Will that work? 2. Do I even need the vent for the double lav? Thanks, Amy
Redwood Master Plumber Messages 7,335 Reaction score 14 Points 0 Location Connecticut Jan 23, 2008 #2 Close but no cigar! On the 2 closest to the verticle drop you have constructed an s-trap. Review your use of horizintal sani-tees.
Close but no cigar! On the 2 closest to the verticle drop you have constructed an s-trap. Review your use of horizintal sani-tees.
Dunbar Plumbing Master Plumber Messages 2,920 Reaction score 11 Points 0 Location Northern Kentucky/Greater Cincinnati Area Website www.koldbreeze.com Jan 23, 2008 #3 The furthest fixture on the drawing is fine only if that vent is 42" up before it goes horizontal. The two lavs need to be vented off tees, combined on the vents and go horizontal as one and on up. That involves 42" or higher as well.
The furthest fixture on the drawing is fine only if that vent is 42" up before it goes horizontal. The two lavs need to be vented off tees, combined on the vents and go horizontal as one and on up. That involves 42" or higher as well.
Jimbo Plumber Messages 8,918 Reaction score 21 Points 0 Location San Diego, CA Jan 24, 2008 #4 All the vents must be 42" above the floor before they go horizontal. The fixture drains must connect to the main with a wye and 45, not the santee shown.
All the vents must be 42" above the floor before they go horizontal. The fixture drains must connect to the main with a wye and 45, not the santee shown.
O orbea1 New Member Messages 10 Reaction score 0 Points 0 Jan 24, 2008 #5 OK, let's try this again. SLightly different Design Horizontal vents will be at least 42" above floor or 6" above flood level of the lav. Is the 90 Ell in the wall going to be OK?
OK, let's try this again. SLightly different Design Horizontal vents will be at least 42" above floor or 6" above flood level of the lav. Is the 90 Ell in the wall going to be OK?
Cwhyu2 Consultant Messages 1,615 Reaction score 22 Points 38 Location Cincinnati OH Jan 24, 2008 #6 Looks good to me.Eccept showervent should same hight as lav vent. Last edited: Jan 24, 2008
O orbea1 New Member Messages 10 Reaction score 0 Points 0 Jan 24, 2008 #7 Thanks. That is actually a third lavatory. But I will make all the vents the same height.
Cwhyu2 Consultant Messages 1,615 Reaction score 22 Points 38 Location Cincinnati OH Jan 24, 2008 #8 Your welcome . thougt was a shower pipe it like the other two good to go.
ltnicks New Member Messages 4 Reaction score 0 Points 0 Location Wisconsin Jan 24, 2008 #9 the 90's will work in this scenario, the drawings look good, only the numbers for pitch, height, minimum, and maximum are left out.
the 90's will work in this scenario, the drawings look good, only the numbers for pitch, height, minimum, and maximum are left out.
Lakee911 I&C Engineer (mostly WWTP) Messages 1,254 Reaction score 1 Points 38 Location Columbus, OH Jan 28, 2008 #10 I see some offset joints. Might get a clog there