If by sealed combustion you mean an modern FVIR wh, with conventional draft hood on top, then the supply of combustion air is even more important than with an older unit. Although the actual requirements have not changed, you might have got by with less than optimum on an old one, and it will be trouble on a new one.
The installation manual, and the National Fuel Gas Code spell it out. Depending on where the closet is, you will need a certain number of suqare inches of ventilation. You need TWO of these inlets, one in the top 14 inches from the ceiling, and one within 14 inches or so from the floor.