Reversed pressure switch

Users who are viewing this thread

Alternety

Like an engineer
Messages
768
Reaction score
0
Points
16
Location
Washington
Does anyone know of a pressure switch I can use with my well system that OPENS the contacts to run the pump and closes them to stop?
 
R

Rancher

Guest
alternety said:
OPENS the contacts to run the pump and closes them to stop?
Sure, just use the contacts to operate a relay, or pump contactor, what you want is a double pole double throw relay, which means you have contacts for either normally open or normally closed, any contractor electrical supply house will have what you need.

Rancher
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
alternety said:
Does anyone know of a pressure switch I can use with my well system that OPENS the contacts to run the pump and closes them to stop?
Go to www.grainger.com and look at stock numbers 6B452, 5B416, 2FG93, 1V630, And 6B437. Perhaps one of them will suit.
 

Alternety

Like an engineer
Messages
768
Reaction score
0
Points
16
Location
Washington
One of the Square D units looks good.

The reason - the motor control uses an open circuit to run. I am not sure why they did that; but they did. The power does not flow through the pressure switch contacts; just a control current.

Rancher - I know. I just want something that looks "regular" to handle it. I have other things to joust with.
 
R

Rancher

Guest
alternety said:
Rancher - I know. I just want something that looks "regular" to handle it. I have other things to joust with.
Can you tell us what the motor control looks like, it seem like you probably have what you already need to do the job.

Rancher
 

Alternety

Like an engineer
Messages
768
Reaction score
0
Points
16
Location
Washington
It is a Baldor BC140. It supplies variable speed DC motor control. It supplies up to 180 VDC at about 11 A.

I am going to check with the factory and see if there is another point inside that would accept the close to run signal. There is a set of pins that allow that but they don't actually remove power from the motor when it is stopped. I found this out experimentally. The motor hums when it is "off".
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
What happens if you use a switch in the normal way to simply disconnect power from the thing that is giving AC to the controller? I guarantee it won't run if there is no AC.
 

Alternety

Like an engineer
Messages
768
Reaction score
0
Points
16
Location
Washington
Switching the DC would circumvent the soft start and I don't believe they recommend switching the output. Switching the input would work but I just have the feeling that it would be better for the controller if it did not keep turning it on and off. I am not sure how soft start will react to this approach either.

I also have to implement low water protection. The source of this signal is a low voltage relay contact. It is a double throw so there is not a problem.

I would really just rather use the provided control points in the controller.
 