i would go with the J5. When you fill the pipes with water close the regulator on the discharge of the pump all the way.If you dont have a regulator you need to get one. You need a minimum of 30 psi back pressure on that jet assembly.You could temporarily use a ball valve off the discharge. Just make sure the ball valve is coming off a tee on the discharge of the pump so you can place a gauge on the top of the tee. In your jet assembly the nozzle should be an A017 and the venturi a AD726. The pressure should come up to like 70 psi. From there start opening the regulator until you have a decent flow of water.
SAM
i would go with the J5. When you fill the pipes with water close the regulator on the discharge of the pump all the way.If you dont have a regulator you need to get one. You need a minimum of 30 psi back pressure on that jet assembly.You could temporarily use a ball valve off the discharge. Just make sure the ball valve is coming off a tee on the discharge of the pump so you can place a gauge on the top of the tee. In your jet assembly the nozzle should be an A017 and the venturi a AD726. The pressure should come up to like 70 psi. From there start opening the regulator until you have a decent flow of water.