Tub to Shower - Venting Question

Users who are viewing this thread

Chanle51

New Member
Messages
9
Reaction score
0
Points
1
Location
NYC
Hi - I'm in the process now of redoing our second story bath, and want to remove the tub and install a shower. (We're in NH.)

Assuming the tub drain is 2" PVC and that I can either move the drain location to the center of the shower pan or that I can find a pan that has the offset, drain....would the venting in place for the tub drain automatically apply to the shower, or would additional venting work be required?

I know this is an elementary question, but I've searched high and low and can't find answers either way.
Thanks a lot!
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
Unless the tub was a shower B4 it was a tub the tub drain piping will B 1.5". Code is 2" for a shower.
 

Chanle51

New Member
Messages
9
Reaction score
0
Points
1
Location
NYC
Thanks for the response Cass. If for the sake of this question we assume that the 1.5" tub drain pipe was actually 2" PVC then would the existing tub drainage and venting design match the needs of a shower, or would different or additional venting be needed?

I do expect to find 1.5" PVC when the tub is out later today.
 
Last edited:

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
If the DWV is 2" and connected to a vent it will work for a shower if you can move the trap without compromising the Joyce's.
 