To prevent copper from touching ductwork?

Users who are viewing this thread

ToolsRMe

New Member
Messages
145
Reaction score
1
Points
0
Location
Colorado
Somewhere recently on this forum someone wrote that copper should not touch ductwork because of the chemical reaction between the two.

Is duct tape adequate protection to prevent the reaction?
 

Dunbar Plumbing

Master Plumber
Messages
2,920
Reaction score
10
Points
0
Location
Northern Kentucky/Greater Cincinnati Area
Website
www.KoldBreeze.com
No. Use foam pipe insulation or something thick to wrap around the pipe.

Tape can eventually wear through if vibration is possible.

Most times when I have to repair water lines that have been in contact with panning or ductwork......it is never in a good spot and always hard to rework the piping.


Those leaks usually take years to surface as well.....they slow leak a long time before you even see the damage come through the ceiling/walls.
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
I would use a peice of cardboard / plastic between them.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
pipe

There is no "reaction" between them since the copper should not be wet. The problem would be movement due to expansion and contraction rather than a reaction or vibration. Anything that separates them, such as pipe wrap tape, will be beneficial, but the ideal thing would be to not have them touching in the first place, even if it is only by the smallest gap.
 

Dunbar Plumbing

Master Plumber
Messages
2,920
Reaction score
10
Points
0
Location
Northern Kentucky/Greater Cincinnati Area
Website
www.KoldBreeze.com
hj said:
There is no "reaction" between them since the copper should not be wet. The problem would be movement due to expansion and contraction rather than a reaction or vibration. Anything that separates them, such as pipe wrap tape, will be beneficial, but the ideal thing would be to not have them touching in the first place, even if it is only by the smallest gap.

hj,

Condensation. Cold incoming water against a warm duct pipe

Hot water against a cold duct work. Either way it causes the piping to sweat.

Next time I find one of these I'll take a picture of both....and the drywall.


What really sucks is that I know for a fact that when I was in new construction I did this sort of thing all of the time to get water lines in an already crowded joist space and didn't put protection between the duct work and pipes. Most cold air returns the piping pierces perpendicular and usually where the holes are touching the pipe cause the leaks.

I feel bad now. :( I wish I would of known now back then. Those people have future plumbing expenses coming.
 

Winslow

Plumber
Messages
445
Reaction score
0
Points
0
Location
Hawaii
you will get electrolysis if copper comes into contact with a dissimilar metal (other than brass) whether there is movement or not or expansion and contraction or not. The water running through the copper pipe will create an electrical current and the pipe will deteriate starting at the point of contact. By the time you realize there is a leak you can have a large portion of paper thin pipe. Milwrap tape, or anything to cause separation (however slight) will prevent electrolysis. using pipe insulation will work well in areas where the copper and dissimilar metals run close together for long runs.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
reaction

The water has to touch both metals in order to become the electrolyte. Water inside the pipe will only cause a reaction between dissimilar metals making up the piping system.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Condensation

Cold water, warm ducts, no problem unless there is moisture in the air, and there should be no moisture inside the walls. Cold water pipe, below the air's dew point, plus moisture will create condensation even without a duct.
 

Winslow

Plumber
Messages
445
Reaction score
0
Points
0
Location
Hawaii
hj said:
The water has to touch both metals in order to become the electrolyte. Water inside the pipe will only cause a reaction between dissimilar metals making up the piping system.


Iv'e done many a repair on looped copper lines that deteriated because they came into contact with nails, rebar, wire mesh, (used when they pour a slab), cast iron pipe, to name just a few. None of these things had water in them besides the looped copper (except the CI drain line) and they all deteriated due to a chemical reaction caused by the copper touching dissimilar metal. It usually takes a long time (although there are exceptions). It happens quite notably when the hot water line contacts thre cold water line (both copper pipe).
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
The reason it takes a long time is slabs trap moisture from the earth and create an atmosphere that will cause the contact points to slowly allow electrolysis to do it's damage even when the area seems dry.
 