Loop vent question: waste connection

Users who are viewing this thread

Riosman

New Member
Messages
23
Reaction score
0
Points
0
Location
San Diego
I'm installing a loop vent for an island sink. This is for a room addition. I would like to make the loop vent waste connection up stream of the sink waste connection. The two books I have show the vent return to the waste line down stream from where the sink connects to the waste line.

Does it matter where the loop vent connects back to the waist line?
Could it even be a different waist line than the sink it is servicing?

Riosman
 

Shacko

Master Plumber-Gas Fitter
Messages
559
Reaction score
1
Points
0
Location
Rosedale, Md
Island vent

A island vent has to hook-up to the waste line after the trap, not upstream. it has to tie into the waste line that the trap is connected to. You usually have to increase the drain one pipe size. Luck.

----------------------------------------------
"If you don't have the time to do it right, where will you find the time to do it over?"
 

Riosman

New Member
Messages
23
Reaction score
0
Points
0
Location
San Diego
The reason for connecting the loop vent return to the waste line upstream from the sink connection to the waste line was to avoid boring through a floor joist. I can still do this by adding two 90's or 45's to get to the other side of the sink connection.
The vent line is 1 1/2 dia and the waste line is 2 inches .

Thanks for the reply

Riosman
 

Phil H2

New Member
Messages
124
Reaction score
0
Points
0
Location
Tujunga, CA
I don't know about the IPC/IRC. But, the UPC does not allow it. It says that connection for an island vent must be made immediately downstream. Also, When connected to a horizontal drain, any vent pipe must take-off above the centerline of a drain pipe.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
loop vent

As a practical matter it doesn't matter which pipe is the drain and which is the vent, as long as the one you decide to use for the vent has a lateral vent which eventually goes out the roof. The lateral pipe is the "vent' and the connection back to the drain is a drain to eliminate any condensation or backup that gets into the loop vent piping.
 

Winslow

Plumber
Messages
445
Reaction score
0
Points
0
Location
Hawaii
This is an illustration of an island sink according to the UPC. The illustration however shows the cleanout on the wrong portion of pipe. It belongs on the vertical section that extends through the roof, which allows you to clean the foot vent.
 

Attachments

  • island vent.bmp
    69.1 KB · Views: 4,297
Last edited:

ToolsRMe

New Member
Messages
145
Reaction score
1
Points
0
Location
Colorado
winslow said:
This is an illustration of an island sink according to the UPC

I am not a plumber ... but that just doesn't look right.

Am I seeing it right that the main drain line ties into the vent stack???? That would block gases from the sink from escaping.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
vent

You are seeing right, and it is correct, although this is just an example. I have installed them with the vent on either side depending on which is easier as far as the lateral vent connection is concerned. Without that drain connection condensation could fill the "trapped" portion of the vent and plug it. It works because the drain does not need air until the sink is almost empty and by that time the horizontal line is no longer full of water that could have risen in the vent pipe and blocked off the lateral vent.
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
An AAV, if allowed where Riosman lives, would simplify thing greatly.
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
So the vent lateral must be sloped as a drain, I assume? (Downward from the stack.) It would slope to the drain line, so it depends on what you call the stack.
 
Last edited by a moderator:

Winslow

Plumber
Messages
445
Reaction score
0
Points
0
Location
Hawaii
Mikey said:
So the vent lateral must be sloped as a drain, I assume? (Downward from the stack.)

Actually that portion of pipe is called the foot vent (UPC terminology), and yes it slopes toward the drain. The loop equalizes the pressure on both sides of the trap to stabilize it.
 

Riosman

New Member
Messages
23
Reaction score
0
Points
0
Location
San Diego
Well I reversed the connection so the vent connects downstream from the waste connection as shown in the picture. It doesn?t seem logical but I noticed all views shown of a loop vent show it this way. I do have a twist. The lateral vent takes off 90 degrees from how the picture is shown to run between the floor joists and to the nearest vertical wall then up and out the roof. The horz.vent line maintains a ¼ per foot slope to the drain.
I wanted to avoid boring several holes thru consecutive floor joists to get out is the reason for the 90 degree approach. Boring the holes would not pass inspection due to violation of the min edge distance of the hole and the joist edge.
 

Winslow

Plumber
Messages
445
Reaction score
0
Points
0
Location
Hawaii
Riosman said:
Well I reversed the connection so the vent connects downstream from the waste connection as shown in the picture. It doesn?t seem logical but I noticed all views shown of a loop vent show it this way. I do have a twist. The lateral vent takes off 90 degrees from how the picture is shown to run between the floor joists and to the nearest vertical wall then up and out the roof. The horz.vent line maintains a ¼ per foot slope to the drain.
I wanted to avoid boring several holes thru consecutive floor joists to get out is the reason for the 90 degree approach. Boring the holes would not pass inspection due to violation of the min edge distance of the hole and the joist edge.


The foot vent has to come off the return vent(the vertical pipe coming down from the top of the loop). You cannot take it off the drain line. (as it sounds by your description.)
 

Winslow

Plumber
Messages
445
Reaction score
0
Points
0
Location
Hawaii
ToolsRMe said:
I am not a plumber ... but that just doesn't look right.

Am I seeing it right that the main drain line ties into the vent stack???? That would block gases from the sink from escaping.

It doesn't look right because you are not a plumber. The sewer gas escapes through the foot vent. The return vent equalizes pressure on both sides of the trap (preventing unequal pressures on either sides of the trap seal. )
 

Riosman

New Member
Messages
23
Reaction score
0
Points
0
Location
San Diego
The foot vent connects to the loop return above the drain just as shown in the picture. I changed the course of the foot vent so it doesnt run in the same direction as the waste drain in order to avoid floor joists. I also took the shortest route to the nearest wall.
 

Winslow

Plumber
Messages
445
Reaction score
0
Points
0
Location
Hawaii
Riosman said:
The foot vent connects to the loop return above the drain just as shown in the picture. I changed the course of the foot vent so it doesnt run in the same direction as the waste drain in order to avoid floor joists. I also took the shortest route to the nearest wall.

That is fine, you should always limit the lenth of a horizontal vent below the flood rim to as short as possible or practical.
 

Phil H2

New Member
Messages
124
Reaction score
0
Points
0
Location
Tujunga, CA
hj said:
As a practical matter it doesn't matter which pipe is the drain and which is the vent, as long as the one you decide to use for the vent has a lateral vent which eventually goes out the roof. The lateral pipe is the "vent' and the connection back to the drain is a drain to eliminate any condensation or backup that gets into the loop vent piping.
hj
Thanks for the practical explanation. I could not think of a reasonable reason why the UPC says the connection should be immediately downstream. I suppose a pedantic bureaucrat could argue that a connection upstrem may be prone to clogging because it is not scoured by the drainage.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
drainage

The possibility of clogging is why the line going through the roof should also have a cleanout in it above the floor level, even though it is not shown in the picture.
 

Riosman

New Member
Messages
23
Reaction score
0
Points
0
Location
San Diego
For the foot vent cleanout above the floor can a San tee be used? The reason is to have as short as possible extension going horz out of the wall. I would prefer a combo at the horz to vertical turn with a cleanout but this would be 2" below the subfloor which violates the above the floor rule. Can this rule be broken?
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
cleanout

I prefer it above the floor so I don't get flooded when the plug is removed, otherwise you can put it anywhere it serves the intended function.
 