If you know how to operate the volt/ohm meter you could do that real easy without having to hook the pump up at all. Just check the voltage, then disconnect them from the pressure switch or control box, twist the ends together and check to ground out at the other end. Then twist just two of them together and check continuity. The wires in the ground if not in conduit should show more than 50,000 ohms to ground minimum. If not, replace them. The 190 feet of wire needs to be put in a metal container filled with water with all uninsulated ends out of the water. Put one probe on the bucket and the other on the ends to check for a nick in the wire. It only takes one.
What brand pump did you install?