Thread: How far can a vent run Horizontal

  1. #1

    Default How far can a vent run Horizontal

    I apologize if this is a stupid question, but I'm having trouble figuring out the answer from my books and code checks, so here goes:

    How far can a vent run horizontal once it get up above your fixtures? For example in the attached picture:

    1) as far as I can tell, Distance "X" needs to be <6 feet

    2) For distance Y and Z, is there limitation before I turn up to the roof, or could I theoretically go across the house?

    A little critic on my plumbing setup would be apprciated as well! Thanks,

    FYI, I'm planning out a full basement bath and bar sink that is across the house from the main stack. I have another stack at the back of the house that I plan to run to, but I believe I need to run a new vent up the nearest wall to the new bath.... I don't think Seattle PLumbing code (UPC) allows side wall venting, which would have been easier.

    Thanks again,
    Nick
    Attached Images Attached Images  

  2. #2

    Default

    In my town, there is no length limitation on Y, Z. However, both sections must be downward sloping to the drain so that condensate any errant water that finds its way into the system has a place to go. There should be no low points.
    (important note: I'm not a pro)

  3. #3

    Default

    Thanks for your help. One more follow-up question. Can I change direction on during that long horizontal run (either Y or Z in the previous picture) as long as I keep that 1/4 per foot drop for condensate?

    I'm probably making more trouble for myself and ought to just run a new vent pipe, but fishing it up the interior wall is a real pain.

    Thanks,
    Nick

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,401

    Default

    I think you'll find that once you are above the flood plane, as long as you have the slope to allow condensation or rain water from the roof to drain, it really doesn't matter where you go with it.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5

    Default

    Ditto. Bend me, shape me, any way you want me. As long as you love me, baby, it's all right!
    (important note: I'm not a pro)

  6. #6
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    The X measurement with upc code would be from the vent to the flange,(six feet or less)

    The vent horizontal could be 1/3 the vertical.

    So if you had 24 feet of vertical, your horizontal could be 8 feet.
    If you go up a pipe size, there is no limit.

  7. #7

    Default

    I'm sorry, now I think I just got confused. Terry, did you just nix what the others were saying? Perhaps you could point me in the direction of the code far that horizontal vent code?

    Thanks
    Nick

  8. #8

    Default

    Never mind, just found it... UPC 904.2... But it says:

    "904.2 No more than one-third (1/3) of the total
    permitted length, per Table 7-5, of any minimum
    sized vent shall be installed in a horizontal position.

    Exception: When a minimum sized vent is
    increased one (1) pipe size for its entire length,
    the maximum length limitation does not apply."

    Am I mis-reading? This appears to say that it is allowed to be 1/3 the TOTAL length, which for a 2" vent would be 1/3 of 120 feet, or 40 feet.
    Last edited by burdick101; 08-01-2006 at 01:51 PM.

  9. #9
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    That's how it appears to read.

    1/3 of total allowed. That would mean that up to 40 feet of 2" could be horizontal without going up a pipe size.

    I wish I had seen that 10 years ago when I was doing a resturant in Bellevue. The inspector didn't see it that way.

    One third of the allowed lenth is much more than 1/3 of vertical.