4" going to the sewer, the house is getting a half bath, wash machine in the basement, kitchensink, dishwasher on the 1st floor and full bath on 2nd.
I've added up 19 fixture units which can be handled by a 3" waste in Massachusetts. I'm not sure if the inspector will want full size from the waste going out to the sewer which is 4". Can I just put a no-hub adapter, cleanout and then transition over to 3"? Or do I have to keep it 4" all the way up and out?
 

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
sewer

You can probably run 3" to a point outside the building, but you should install cleanouts where you make the transition, otherwise you will never be able to snake the 4" pipe using the 3" one.
 