Thread: 3" flue for water heater failed inspection

  1. #1
    In the Trades plumbernj's Avatar
    Join Date
    Aug 2005
    Location
    New Jersey
    Posts
    27

    Default 3" flue for water heater failed inspection

    Original tank... a 40 gallon nat gas Bradford water heater with a 3" flue.

    Did a replacement with another 40 gal gas 3" flue, same 40,000 btu output...and it failed inspection because the inspector now wants a 4" flue to the chimney.
    Can soneone point me the the gas or mechanical code so this doesn't happen to me again?

    In NJ.

  2. #2
    I&C Engineer (mostly WWTP) Lakee911's Avatar
    Join Date
    Aug 2005
    Location
    Columbus, OH
    Posts
    1,328

    Default

    You're best asking the inspector who failed you for the code reference.

    Jason

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Most codes are based on, or invoke, the National Fuel Gas Code. A 3" flue for a 40,000 BTU WH would be typical in most installations. The WH manufacturer probably specifies a 3" but also refers to the above code. You said you are venting into a chimney, and so some combination of factors here is adding up to him wanting a 4" . He should be willing to explain.

  4. #4
    In the Trades Bob NH's Avatar
    Join Date
    Oct 2005
    Location
    New Hampshire
    Posts
    3,307

    Default

    It's New Joisey! He was probably expecting something more than than a flue.

  5. #5
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,244
    Blog Entries
    1

    Talking 3 inch hood vent

    its interesting that they throw such a hissey fit over this....

    especially when the hood of the water heater actually
    comes off at 3 inch..anyway...........

    even if you increase it to 4 above the hood vent ,
    whats the benefit??? since its already been restriceted?

  6. #6
    General Contractor Carpenter toolaholic's Avatar
    Join Date
    Jul 2005
    Location
    Marin Co. Ca.
    Posts
    829

    Default simple test

    turn the water heater up all the way so burner comes on.
    now take a butane gas log lighter or match and run the flame above the bonnet opening below flue. flame drawn in, good flame blown out bad. also run any additional appliances on the chimney at the same time.

  7. #7
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    Quote Originally Posted by toolaholic
    turn the water heater up all the way so burner comes on.
    now take a butane gas log lighter or match and run the flame above the bonnet opening below flue. flame drawn in, good flame blown out bad. also run any additional appliances on the chimney at the same time.
    This test, even if it turns out O.K., most likely, won't change the inspectors mind.

    Did you install it your self or did a plumber do it. If you pulled the permit and did it your self the inspector is just giving you a hard time because he doesn't like DIYers. Thats my guess.

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default flue

    And it is one more reason why few water heater replacements are done with a permit.

  9. #9
    I&C Engineer (mostly WWTP) Lakee911's Avatar
    Join Date
    Aug 2005
    Location
    Columbus, OH
    Posts
    1,328

    Default

    Quote Originally Posted by Cass
    Quote Originally Posted by toolaholic
    turn the water heater up all the way so burner comes on.
    now take a butane gas log lighter or match and run the flame above the bonnet opening below flue. flame drawn in, good flame blown out bad. also run any additional appliances on the chimney at the same time.
    This test, even if it turns out O.K., most likely, won't change the inspectors mind.

    Did you install it your self or did a plumber do it. If you pulled the permit and did it your self the inspector is just giving you a hard time because he doesn't like DIYers. Thats my guess.
    You'd also want to close all windows and doors, turn on the dryer, range vent, bathroom vent, etc and all other normal air discharge points in the house.

    Jason

  10. #10
    In the Trades plumbernj's Avatar
    Join Date
    Aug 2005
    Location
    New Jersey
    Posts
    27

    Default

    No, we are a plumbing company. This happenned in Barrington, NJ.

    Oh, and we had to get a permit. Homeowner wanted one.

  11. #11
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    Since you are in a business where you probably must work with this inspector on a regular basis, you sure don't want to get on his bad side. I do think it would be fair for you to ask him what code he applied. Perhaps approaching him with a positive attitude explaining that you need to know so that you don't have a similar problem in the future. If you were to confront him in a manner that would put him on the defensive, you would get no where.

  12. #12
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,244
    Blog Entries
    1

    Talking permits are a pain and unfair

    it really pisses me off that Lowes, Home Depot, ******* ect

    can sell you a water heater and let you do it yourself wether you know

    what you are doing or not......


    without you having to obtain any kind of permit what-so -ever and get away with it

    But a plumber who KNOWS what they are doing gets a permit and look at all

    the petty greif that comes your way..........

  13. #13
    DIY Member brianj's Avatar
    Join Date
    Nov 2005
    Location
    Maryland
    Posts
    35

    Default

    Quote Originally Posted by master plumber mark
    it really pisses me off that Lowes, Home Depot, ******* ect

    can sell you a water heater and let you do it yourself wether you know

    what you are doing or not......


    without you having to obtain any kind of permit what-so -ever and get away with it

    But a plumber who KNOWS what they are doing gets a permit and look at all

    the petty greif that comes your way..........
    The plumber who installed mine didn't pull a permit. Neither did the guys who did the roof. As bassakward as this City is, I understand why they don't bother though...

  14. #14
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default vent

    Quote Originally Posted by Lakee911
    You'd also want to close all windows and doors, turn on the dryer, range vent, bathroom vent, etc and all other normal air discharge points in the house.

    Jason
    And how would a 4" flue instead of a 3" make any differnce in all that?

  15. #15
    General Contractor Carpenter toolaholic's Avatar
    Join Date
    Jul 2005
    Location
    Marin Co. Ca.
    Posts
    829

    Default this simple test was done by a factory service rep

    years ago. i had just installed a new w. h. ,75 gal a.o. smith and it wouldn't lite off. i believe he replaced the burner assembly. the old 3" chimney wasen't large enough. i installed a 4 " right away. the flame moved away from the chimney. If you read my post ,you'll see I never stated this a fix
    for a new jersey inspector. My brother in law built his home there. the insp was a flamming a hole. I would have put his face on a milk carton