Thread: Cleanouts
    DIY Member Hazel's Avatar
    Jan 2006
    Washington
    Default Cleanouts
    Does a lavatory sanitary Tee / p-trap flange that drains into a combo Wye in the middle of a horizontal drain run with more than 135 deg turns count as a cleanout? Thanks!
    Hazel
    Apr 2005
    That is a loaded question. Are you asking in reference to code or just if it will work?
    Cleanouts should be sized to the main line they connect to. Meaning, if that 1.5" line leads into a 3" main line, then the cleanout should be sized @ 3" before it enters the concrete floor.
    That probably didn't answer your question.
    Jan 2006
    Washington
    Default Is it allowed per code?
    The horizontal run in question is 2", so a 1.5" lav inlet satisfies the cleanout size requirement. Does it qualify as a cleanout per code though? Thanks.
    Hazel
    Default co
    [QUOTE=Hazel]Does a lavatory sanitary Tee / p-trap flange that drains into a combo Wye in the middle of a horizontal drain run with more than 135 deg turns count as a cleanout? Thanks!
    Not always, because it is only 1 1/4" or 1 1/2" and a cleanout has to be the same size as the pipe or 4" whichever is smaller. And some codes do not recognize any cleanout that requires that the drain be disassembled to use it. WE always have to install a cleanout tee below the fixture connection tee in the vertical riser if that fixture needs a cleanout.
