Replacing or coating galvanized pipes?

Users who are viewing this thread

smcgowan65

New Member
Messages
4
Reaction score
0
Points
0
My sister lives in a house built in the 70's, and their pipes have finally gotten to the point where there's really low flow all over the house (it's a one story). We have been debating the efficiency of replacing all the pipes with copper, or just doing the epoxy sealer (not sure of the name, but the local radio fix-it guy here is all over it like white on rice). Our primary concern is the fixing part--if the pipes are replaced, we'll have to do all the cosmetic repair (green board, hardibacker, sheetrock, tile, paint, texture, and so on). The work sounds daunting. Has anyone out there replaced their galvanized piped with copper? How did it go? Was it horrible? Was the mess manageable? Has anyone else done the inside the pipe coating? What's that like? I have heard rumors of funky tasting water afterward. We are looking for a good solution to which we can contribute sweat equity, but not to the point of unreasonableness since we both have full time jobs.
 

Dunbar Plumbing

Master Plumber
Messages
2,920
Reaction score
10
Points
0
Location
Northern Kentucky/Greater Cincinnati Area
Website
www.KoldBreeze.com
Well, here is the scoop; someday you will replace those water lines, it is inevitable. That system you are talking of would probably clog them up for good. That epoxy is mainly used for copper piping and most times they won't discuss what happens when there is a total blowout of the copper tubing in the wall or ceiling (they have to go in and replace a section like you would any other type of piping) and this is what you are trying to avoid to begin with.

As with any water line system in a home there will be removal/patching of walls/ceilings/floor depending on the areas affected. In galvanized systems usually the last 3 fittings leading to the fixture usually clog up, cleaning/removing them would probably restore flow that is sufficient to operate the fixtures. Most galvanized vertical lines remain clear. Funky tasting water is probably flux; that can be avoided by proper installation without excess flux. Majority of people have full time jobs so your time spent would be around work. Do a section at a time, always connect to dielectric unions when reconnecting to galvanized until it is all removed.

Do not flux up a run of pipe/fittings and not solder the connections right away. This can cause quality issues with the solder joints. I cannot figure out why people do this to begin with. :confused:

If cost is a issue, I advise inspecting the last 3 fittings leading to the faucet/fixture; you'll see that they will be clogged most times.
 

smcgowan65

New Member
Messages
4
Reaction score
0
Points
0
Love the cowbell.

So, just to clarify, we can replace the last three fittings and that should be good enough to restore water flow? I think my dad said that hot water was more reactive than cold (or vice versa--they're not my pipes; I only get involved in the "crisis" discussions at family dinners; and Easter is coming...).I guess what we're trying to decide is: do you do the "quick" fix, or do you just go and replace all the hot (or cold) water pipes? I am trying to get a feel for how much of a mess is involved in breaking through a tiled shower to replace all that galvanized pipe.

The funky taste people complain about if AFTER they coat the insides of their galvanized pipes with the epoxy. The pipes are "blown out" (whatever that is) prior to the coating. I have heard that the blowing out can actually remove sludge which has blocked pinhole leaks in glavanized pipes, too; yet another thing to worry about. The whole epoxy system is running about $2300.....
 

Dunbar Plumbing

Master Plumber
Messages
2,920
Reaction score
10
Points
0
Location
Northern Kentucky/Greater Cincinnati Area
Website
www.KoldBreeze.com
That is news to me that you can epoxy a galvanized line. How it can remove 85% blockages is amazing. When I have my first heart bypass I am going to tell my doctor about this technique.

I would shut the water off, remove the supply line from the fixture to the isolation valve under the sink/toilet. Then, CAREFULLY remove the valve. If you are dealing with deteriorated galvanized feed lines the threaded part of the pipe is the weakest part; they can snap off easily if you are not careful. If the pipe leading out of wall is completely clogged, take it back to the next turn of direction. If that next fitting leads to a vertical pipe, that vertical pipe is probably in decent shape and worthy of reconnecting. This though is a "trial by error" procedure and you are trying to avoid the error part as much as possible. Whether you have the hands of trained plumber or the hands of a monkey, this piping can have weak spots in the threaded parts or a pipe can break that will lead you to the next in-line threaded connection. That can turn a small job into a large one real quick. Just think of the snowball effect.

What is weird is I have seen either hot or cold lines clog up completely. I would think for sure the hot would be first to go but sometimes the cold and not the hot will be affected. I've done a great deal of galvanized to copper changeouts in my years as a plumber. Very rarely does any galvanized pipe stay in a home. It always eventually goes bad/restricts flow.
 

Dunbar Plumbing

Master Plumber
Messages
2,920
Reaction score
10
Points
0
Location
Northern Kentucky/Greater Cincinnati Area
Website
www.KoldBreeze.com
smcgowan65 said:
The funky taste people complain about if AFTER they coat the insides of their galvanized pipes with the epoxy. The pipes are "blown out" (whatever that is) prior to the coating. I have heard that the blowing out can actually remove sludge which has blocked pinhole leaks in glavanized pipes, too; yet another thing to worry about. The whole epoxy system is running about $2300.....


If you can, read the small fine print in the contract about the guarantee and exclusions that this service provides. You will probably realize through very well written logic (lawyer speak of course) that you can't make a silk purse out of a sow's ear, and they know that their product can only do so much.
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
Let's Apply Some Logic

You have low flow all over the house which you attribute to galvanized pipe.

Galvanized pipe fails when the internal galvanizing (zinc) is eaten away by corrosion, and iron oxide and other precipitates build up in the pipe. That buildup is called "tuberculation". It can virtually fill the pipe because the rust takes up much more space than the iron it replaces.

At the bottom of the page at the link below there is a picture of an iron pipe nearly closed by tuberculation. And that is a large pipe.
http://plasticpipe.org/mi/water/index.php

The only way you will restore the flow capacity in the pipe is to:
1. Remove all of the tuberculation, or
2. Replace the pipe.

If you were to manage to remove the tuberculation, you would still have a rusty pipe. That is what the epoxy is for.

HOWEVER; all of the REPUTABLE epoxy coating suppliers require that the steel be sandblasted to white metal before the epoxy coating is applied. That is not possible inside a water pipe in your house.

The best they will do is run some acid through your pipe to remove enough of the rust to increase your flow, do something that they will call "coating" on the rust that remains in the pipe, and quickly cash your check before you notice that they didn't really solve the problem. They will do nothing about the joints that will fail more quickly because of the acid in the joints.

Do yourself a big favor and replace the pipes with copper.
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
There's always a "new and revolutiontionary produce" that will (a) restore compression to a worn out engine, (b) melt hundreds of pounds of fat without effort, (d) rejuvinate rusted out pipes. Who needs a mechanic, a diet, or a plumber! We Americans are brainwashed to think everything should be quick and easy and can be found in a package or can. Please don't be suckered into this scam. Replacing some fittings might marginally improve the situtation briefly, but face the facts. You will have to repipe the entire house sooner or later, and more likely sooner that later.

Galvanized pipes at one time were the only thing available. True, in time they would corrode and cut water flow, but it's all we had. Today, no one would even consider galvanized pipes for at least a couple of reasons. First, it would be far more expensive to pay the labor for all of the cutting and threading. Everytime I use black iron pipe for natural gas, I am reminded of this. Second, it would be just plain stupid to install pipes that will corrode shut in time.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
The system you may refer to is the Ace Duraflow. They sandblast the insides of the pipe, then flow in the epoxy.

Was your house bulit in 1870? In these parts, they stopped using galv. in 1950. All copper after that.
 

Shacko

Master Plumber-Gas Fitter
Messages
559
Reaction score
1
Points
0
Location
Rosedale, Md
Galve. pipe

Sounds bogus to me, you are going to spend $2300 to repair pipe that you will be tearing out in a short time? [You will be tearing it out!]. Bite the bullet now and replace. Use the $2300 for new pipe. Luck.
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Urban myth dept.

RUGGED said:
If you can, read the small fine print in the contract about the guarantee and exclusions that this service provides. You will probably realize through very well written logic (lawyer speak of course) that you can't make a silk purse out of a sow's ear, and they know that their product can only do so much.


Actually, you can make a silk purse out of a sow's ear: http://libraries.mit.edu/archives/exhibits/purse/index.html
 

Sjsmithjr

In the Trades
Messages
314
Reaction score
1
Points
16
Location
Knoxville, Tennessee
Galvanized Pipes after 1950?

A little off toppic, but sometime during the mid 60s (1966?) there was a shortage of copper pipe in the U.S. A lot of homes got built with galvanized instead of copper, and around the same time the plastic DWV industry was born.

Also, some "old timers", much as it is today, probably never made the switch to copper and stuck with what they knew.

-Sam
 

Paul Hill

New Member
Messages
1
Reaction score
0
Points
1
Location
Texas
Hey, I have done some investigating on this subject. The ACE DuraFlo was pacifically as an epoxy liner for rusty galvanized pipe. They would not use it in a copper system. as copper doesn't rust. If done right it appears to have several advantages over repippeing. We are in the process of selecting one of two companies that does this process in the Houston area. I'm waiting for a list of customers that have had this done. I'm sure all of the floks on the list will be happy with the results.

I hope this helps.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
They do NOT "reline" copper pipes because of rust, they do it because of erosion or chemical reaction. With galvanized, the first thin you need is credulity that the abrasives will reach EVERY section of piping and remove the corrosion inside. You do this by faith since there is no way to inspect them afterwards. THEN, you also need faith that the epoxy does reach everywhere in the piping and adheres to the pipe's surface, and NO ONE can give you that guarantee.
 

Craigpump

In the Trades
Messages
2,436
Reaction score
158
Points
63
Location
Connecticut
the ONLY way to clean the insides of the pipes is to circulate a slurry of abrasive material, race engine builders do it all the time to smooth out the ports in manifolds and cylinder heads. To do the same thing with old galvanized piping would be expensive, time consuming and probably not done up to your expectations.

Coating the pipes sounds rather dubious as well. How is the epoxy going to adhere to a wet pipe? How do you know the entire system will be coated?

This sounds like a real con game to me.

I would repipe and know exactly what's behind my Sheetrock.
 