Bad Check Valve? Pressure tank drains during power outage.

Users who are viewing this thread

JDM

New Member
Messages
6
Reaction score
0
Points
0
Location
Snohomish County, WA
We've been in our new house about a year now. We finally had a sustained power outage. When I woke in the morning there was no water pressure. I checked the pressure tank and found it was empty! This has happened twice now. I assume it is the check valve (located a foot or two below ground at the well head). This must be a very slow leak as the pressure sure doesn't drop fast enough for me to see it at the gauge. It took many hours.

Is this likely to be a bad check valve? (the only other option I can think of is a leaky Pex line to the house...)

Can check valves be repaired or is it best to replace it?

I'm not certain but it may be horizontal. Is there a preferred orientation?

Any plumber types in the Monroe, Washington area on the forum?

There is certainly a lot of info in the forum and I apologize as I'm sure the answers are here somewhere.........

Thanks!
Joe
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
If the pump is in the well, it has a check valve in it, which should be the only check valve needed. With that, the leak could be in the drop pipe or the pitless adapter.
 

JDM

New Member
Messages
6
Reaction score
0
Points
0
Location
Snohomish County, WA
Good point... The pump is in the well (~180ft). I guess I'll be digging things up to check the valve and the pitless adapter. Thanks! - Joe
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
Before you go digging it up for such a slow leak, have you confirmed there is no usage in the house? A leaking toilet flapper or an R/O filter? A softener leaking to drain?

If you have a reliable shutoff between the tank and the house, try turning it and the pump off to see if you still lose pressure.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Before you go digging it up for such a slow leak, have you confirmed there is no usage in the house? A leaking toilet flapper or an R/O filter? A softener leaking to drain?

If you have a reliable shutoff between the tank and the house, try turning it and the pump off to see if you still lose pressure.


Good Advice.


What is "a sustained power outage" ?

The pump should fill the tank, after power is restored.

It was most likely used while the power was off.


Good Luck.
 

JDM

New Member
Messages
6
Reaction score
0
Points
0
Location
Snohomish County, WA
Yes, more great advice. I don't think it was usage in the house as we went to bed just after the power went out. Also, when I got up in the morning I found no pressure so I checked the pressure tank. I could easily rock it indicating it appeared to be completely empty. Let me know if I'm wrong but I didn't think the residual pressure would be sufficient to completely drain the tank through an iron filter and a softener, especially since it is in the crawl space 1 floor down. The pump did fill the tank quickly once I got the generator going.

Please know that I (and a host of others like me) truly appreciate the time y'all spend on the forum to answer our rookie questions! Thanks!
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
Let me know if I'm wrong but I didn't think the residual pressure would be sufficient to completely drain the tank through an iron filter and a softener, especially since it is in the crawl space 1 floor down.

The precharge pressure above the bladder would completely empty the tank, even it the water had to go up a floor or more.
 

JDM

New Member
Messages
6
Reaction score
0
Points
0
Location
Snohomish County, WA
The precharge pressure above the bladder would completely empty the tank, even it the water had to go up a floor or more.

I didn't anticipate that. Looks like I'll check both sides of the system before I start digging holes! Our filter & softener have Fleck 7000 SXT valves. Maybe they operate when the power is out and flushed one of the tanks? One of them has a flow indicator. That will be my first check.

THANKS!!
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
I didn't anticipate that. Looks like I'll check both sides of the system before I start digging holes! Our filter & softener have Fleck 7000 SXT valves. Maybe they operate when the power is out and flushed one of the tanks? One of them has a flow indicator. That will be my first check.

THANKS!!


I think the valve will stay in whatever position it was when the power fails.

A leaky Toilet valve can use a lot of water in the long run also.


Good Luck
 

Reach4

Well-Known Member
Messages
38,798
Reaction score
4,412
Points
113
Location
IL
I would turn off power to the pump, and monitor how quickly pressure drops with no known water consumption. See if it takes 20 minutes or 6 hours to lose pressure. Note how big your pressure tank is.

Also, consider shutting the valves at the toilets during this test.
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
You should have one main shut off after the tank. Closing that would isolate whether the leak is inside or outside.
 

jimmy klotz

plumber, electrician, carpenter
Messages
2
Reaction score
0
Points
1
you should isolate the leak first shutting off the main at the tank is a great way to start and if the tank still drains, change the check valve at top.. i highly doubt a leak in the house because you would notice the pump running every so often without any water being ran..
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
I don't recommend a second check valve anywhere in the system, and in many states it is illegal. A check up top may stop the tank from leaking back, but if the check down on the pump is leaking, you will either start getting air in the lines or it will cause a loud water hammer "pop" when the pump starts.
 