Bathtub venting

Users who are viewing this thread

dtms

New Member
Messages
13
Reaction score
0
Points
1
Location
Massachusetts
I need to run my trap arm from the p trap to the main drain under the tub so it runs parrallel to the tub (looking at tub, tub drain is on left and main line i'm draining into is on the right running perpendicular to the tub). Can i attach a vent in the trap arm with a 45 wye say 3' from the p trap so the wye goes up but at a bit of an angle so i can go towards the back wall of the tub and up the back wall of the tub to tie into a vent in the ceiling? I'm a little confused how else to do it.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
It's dangerous to your financial health to do your own plumbing in MA, but a vent must go up above the floor plane of the highest fixture or 42" whichever is higher before it can turn horizontal. On a two inch drain, that connection must be made within 5' of the trap, it gets smaller or bigger depending on the drain line size.
 

dtms

New Member
Messages
13
Reaction score
0
Points
1
Location
Massachusetts
Thanks for the reply. So does the wye have to go straight up or can it go more towards the back wall of the tub as long as that piece between the wye and the 90 going up into the wall is pitched. Is this a common way of venting tubs or is there a more common way that i'm missing?
 

dtms

New Member
Messages
13
Reaction score
0
Points
1
Location
Massachusetts
Thanks for the advice Jim. I live in MA but this is a vacation home in ME i'm working on. So you are saying i would need to come straight up from the arm thru the floor and then i can go horizontal over to the wall. Is there a better option that i'm missing?
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
The wye, (and the vent) must be turned up at least 45 degrees. If you run the drain under or close to the wall, this should not be a problem.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
However it goes up, it must go up at least the 42" before it can turn horizontal...45 or greater is considered vertical for these purposes.
 

dtms

New Member
Messages
13
Reaction score
0
Points
1
Location
Massachusetts
I think I understand. So run the p trap and the arm over towards the back bathtub wall so when i come off the arm with the wye i can basically go straight up into the wall. Is that the idea?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Anything 45-degrees or higher is considered vertical for this purpose, and that link must be within the specified distance based on the size of the pipe.
 