Armoured Cable - Ground
Chefwong
District of Columbia
The AC on the cable serves as the ground in my house circuit runs. Steel boxes-mc/bx cable.
I'm looking at the wire run that the spark did for our HVAC. Ran flex to a J Box. 3 Wires *2 hots, 1 neutral*. Than ran pipe to the HVAC. Spliced/Extended the wires in the J Box and added a ground terminal in here and added a ground in the conduit leading to the HVAC.
I don't really run conduit much.
I'm adding a sub panel off my main panel.
Plan to connect the 2 via Flex and just the standard Squeeze Flex Connectors on the Sub Panel.
No need to run a seperate ground, ground bushing, etc etc right ?
Stuff
Pennsylvania
Regular flex conduit can be used as ground up to 6 feet and 20 amp or less only.
Chefwong
Interesting...The spark than ran it to the J Box, I would estimate a good 15-18 feet. Then from the J Box leading down to the HVAC.....another 20-25 feet from there,
Because fo the way the armored cable connects to the boxes, it CAN be a 'high resistance' connection and not a very good conductor for a grounding circuit. In fact, given that the panel box is painted, the meta covering l may only be making "marginal" contact with the bare metal as the connector is fastened to it.
ActionDave
Electrician
Colorado
That's fine, AC cable has a wire in the sheathe that shorts the coils to make it a proper equipment ground. BX is a brand name AC cable. MC is different, it has a green insulated wire in it for equipment grounding.
What size wires? What kind of flex? What kind of pipe/conduit? What are the distances in each segment?
You need an equipment ground/green in the flex. You don't need ground bushings.
Chefwong
I was planning to add a ground wire, but then I was looking at how the sparky ran the HVAC - and I was like , well, if the flex is good enough for the pro, then why do I need to pull the ground for this .
For the HVAC, the run looks like this
Main Panel - Flex Run to J Box. 6AWG - 2 Hots and a Neutral ( I did not check but it looks to be ALU flex)
J Box - added a ground ring to J Box and added a ground wire
The length from J Box to HVAC is about 25 feet or so