Thread: 2 grounding/bonding questions

  1. #1
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default 2 grounding/bonding questions

    1) Just had a short debate with my local inspector on a job I am bidding. The house is from 1947 and the wiring is all in steel flex conduit.

    He told me that flex conduit cannot be used as the ground for more than 6'. I always understood that to apply when the ampacity of the circuits inside were greater than 20amps. For conventional branch circuits around a house, I had understood that the flex conduit was indeed the ground, no matter how far from the panel it runs.

    2) May well be installing a 50 amp sub panel in an outbuilding. I don't need to run a ground/bond back to the main panel, or has that changed of late? I expect to drive two ground rods and call it good.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    Flex steel conduit makes for a lousy ground. I wouldn't use it for that even it if was allowed. The house I grew up in has that, and corrosion over the years just makes it totally useless.

    I'd run a ground back to the main panel. I do not think it will pass current codes without one. You still need the ground rods on the outbuilding. The grounding is for primarily lightning surge control. The actual ground wire provides a safety path for tripping the fuse or CB...a ground rod is not sufficient for that.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,142

    Default

    AC listed cable is approved for the equipment ground, FMC or LFMC is only approved for 6 feet when used with grounding fittings.

    Sub panel will need a ground back to the main panel AND grounding rods at the sub.

  4. #4
    DIY Senior Member bluebinky's Avatar
    Join Date
    Aug 2011
    Location
    Santa Clara, CA
    Posts
    354

    Default

    The sub panel will also require a neutral bus that is not bonded to ground -- only connect ground and neutral at the main panel.

  5. #5
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    250.32(A)(A) Grounding Electrode. Building(s) or structure(s) supplied by feeder(s) or branch circuit(s) shall have a grounding electrode or grounding electrode system installed in accordance with Part III of Article 250. The grounding electrode conductor(s) shall be connected in accordance with 250.32(B) or (C). Where there is no existing grounding electrode, the grounding electrode(s) required in 250.50 shall be installed.

    250.32(B)(1) Supplied by a Feeder or Branch Circuit. An equipment grounding conductor, as described in 250.118, shall be run with the supply conductors and be connected to the building or structure disconnecting means and to the grounding electrode(s). The equipment grounding conductor shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. The equipment grounding conductor shall be sized in accordance with 250.122. Any installed grounded conductor shall not be connected to the equipment grounding conductor or to the grounding electrode(s).

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    That reads like something written by a lawyer, or an engineer.
    Licensed residential and commercial plumber

  7. #7
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,642

    Default

    Quote Originally Posted by hj View Post
    That reads like something written by a lawyer, or an engineer.

    Written by a engineer and a lawyer would not understand it.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  8. #8
    DIY Senior Member bluebinky's Avatar
    Join Date
    Aug 2011
    Location
    Santa Clara, CA
    Posts
    354

    Default

    Written by a committee of Engineers based on current engineering best practices and more than a century of field experience from people like HJ and JW.

    The wording is the way it is to keep Lawyers from doing electrical installations and then successfully arguing that they did it correctly.

  9. #9
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    Words, and those especially in English, often have slightly different connotations because most of them were absorbed from other languages. As a result, writing something that is as unambiguous as possible, can end up sounding strange since most people do not talk that way. The goal, not always achieved, is to make it as unambiguous as possible so that once you do understand it, there is only one 'right' way to perform the task.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #10
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by jwelectric View Post
    250.32(A)(A) Grounding Electrode. Building(s) or structure(s) supplied by feeder(s) or branch circuit(s) shall have a grounding electrode or grounding electrode system installed in accordance with Part III of Article 250. The grounding electrode conductor(s) shall be connected in accordance with 250.32(B) or (C). Where there is no existing grounding electrode, the grounding electrode(s) required in 250.50 shall be installed.

    250.32(B)(1) Supplied by a Feeder or Branch Circuit. An equipment grounding conductor, as described in 250.118, shall be run with the supply conductors and be connected to the building or structure disconnecting means and to the grounding electrode(s). The equipment grounding conductor shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. The equipment grounding conductor shall be sized in accordance with 250.122. Any installed grounded conductor shall not be connected to the equipment grounding conductor or to the grounding electrode(s).

    JW. You did not actually answer either of my questions, I think.

    1) Does the steel flex conduit count as "an equipment grounding conductor" still? Obviously, back in 1947, it did. And if so, I would be grandfathered in.

    But if it is no longer permissible, even on 20 amp or smaller circuits to rely on the flex conduit as the ground path, and that a separate conductor needs to be pulled, in say, a re-wire, then that is news to me, and the inspector for the extensive rewire I did a few months back in an adjacent city certainly missed the boat on calling me out on it. Granted, that was built in '28 with black gas pipe (ships were wood and men were iron). He had me installing arc faults but no separate conductor. I certainly found low resistance to ground in my tests.

    So, is it acceptable to use the conduit as a ground, or need I run a specific (green) conductor?

    1a) And as a separate question: nearly none of the circuits in the house I am looking at just now are showing a valid ground at the receptacles. The ground at the main panel reads fine. In a house that is going on 70 years of age, is it a reasonable assumption that the interface of the conduit, the connectors and the boxes has all so completely corroded that no reliable ground is available.

    I am writing a document on behalf of the buyer to squeeze concessions from the seller for upgrades, and I would as soon not be talking out of my ass.

    2) For the out building sub panel, I know that I need ground stakes, and that that has been the standard for decades or more.

    But is there a NEW requirement for a grounding conductor to bond the grounding buss bar in the sub panel to the ground/neutral buss bar in the main panel?

  11. #11
    DIY Senior Member Reach4's Avatar
    Join Date
    Sep 2013
    Location
    IL
    Posts
    1,251

    Default

    Quote Originally Posted by jwelectric View Post
    Any installed grounded conductor shall not be connected to the equipment grounding conductor or to the grounding electrode(s).
    What are the implications of this?

  12. #12
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    quote; What are the implications of this?

    On the surface, it would appear that the grounding element just terminates in the air because it cannot be connected to anything.
    Licensed residential and commercial plumber

  13. #13
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Homeowner

    If the armor of AC cable has a bonding strip that is included in the folds of the armor then the cable armor can be used as an equipment grounding conductor. Back in 1947 there was no requirement to install an equipment grounding conductor with the circuit conductors so to presume that the armor is a grounding path would be futile.

    As a sworn code enforcement official should someone in my jurisdiction be replacing receptacles in such an installation as you describe then the two wire receptacles would be replaced with GFCI devices and labeled no EGC as well as Arc Fault protection for the circuit.

    For several decades now an equipment grounding conductor has been required for feeders to a remote building if there is any other electrical path between the two buildings such as telephone or other utility or even a chain link fence that is attached to both buildings. I have never in 47 years not installed an EGC with the feeders as this is the low impedance path to cause the breaker to trip or the fuse to blow. Earth is not a low impedance path and will not clear a fault.

    Also Part II of Article 225 mandates that one of four minimum feeder circuits to be installed and 50 amps is not one of them. If the feeder is going to be larger than 30 the next smallest size allowed is 60 amps, see 225.39 for more information on this subject.


    Reach4

    The groundED conductor is the neutral as outlined in Article 200 and the groundING conductor is the fault clearing conductor outlined in Article 250

  14. #14
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    JW.

    Thanks. I'm not referencing AC, but rather conduit with separate conductors pulled in.

    But, yes, I had been expecting to pull a dedicated ground/bond wire to the sub panel.

  15. #15
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Homeownerinburb View Post
    1) Just had a short debate with my local inspector on a job I am bidding. The house is from 1947 and the wiring is all in steel flex conduit.
    I am sorry but I took this statement to mean you were talking about what everyone calls the old BX cable which was AC cable

Similar Threads

  1. Grounding electrode/bonding question
    By fotto in forum Electrical Forum discussion & Blog
    Replies: 13
    Last Post: 10-14-2012, 10:37 AM
  2. Grounding or Bonding Jetted Bathtub
    By seegee in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 05-21-2012, 06:34 PM
  3. Copper pipe grounding/bonding - how to?
    By Copper Bahamas in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 12-31-2010, 08:56 AM
  4. bonding/grounding and pex
    By peltaz in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 10-23-2009, 05:39 AM
  5. Grounding, bonding, potential??
    By hammerslammer in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 08-21-2007, 09:51 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •