heat pump problem

Users who are viewing this thread

khalsa

New Member
Messages
7
Reaction score
0
Points
1
Location
MD
when i turn the heat on my thermostat the heat pump doesn't come on outside. i can see it start for about a second (the fan moves a tiny bit) and then it stops. it's a carrier performance series heat pump (25hcc542a300). any ideas on where i should start looking?

thanks!
 

khalsa

New Member
Messages
7
Reaction score
0
Points
1
Location
MD
it's around 28 F outside and my other heat pump is running fine.
 
Last edited:

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
You may want to feel the compressor and determine if the Crankcase heater is working.

You may have a bad capacitor.

Can you hear the compressor safety overload click when it does not start ?
 

khalsa

New Member
Messages
7
Reaction score
0
Points
1
Location
MD
You may want to feel the compressor and determine if the Crankcase heater is working.

You may have a bad capacitor.

Can you hear the compressor safety overload click when it does not start ?

I was missing it before, but the fan on the heatpump actually runs for 7-8 seconds every time I turn the thermostat off and back on (after 5-10min or so) as it's turning off I can hear what sounds like pressure releasing and a single small click sound (is that the internal overload?) as the fan is near to a stop.

Any ideas? I think I need to call this in, but I'd like to give them an idea what the problem might be.

The unit's compressor is under warranty, but the rest is past. Should I talk to Carrier first?
 
Last edited:

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
You may be hearing the head pressure equalizing in the compressor, after it kicks off on overload. The Reversing Control Valve may be stuck. It could be a number of things.

Some units are not made to run below freezing, not sure about that one. I did not find much info on the model number that you provided. Below 32F and efficient drops way down.

Is your Aux heating strips working ?

It may be best to call the Man.


Good Luck.
 
Last edited:

khalsa

New Member
Messages
7
Reaction score
0
Points
1
Location
MD
You may be hearing the head pressure equalizing in the compressor, after it kicks off on overload. The Reversing Control Valve may be stuck. It could be a number of things.

Some units are not made to run below freezing, not sure about that one. I did not find much info on the model number that you provided. Below 32F and efficient drops way down.

Is your Aux heating strips working ?

It may be best to call the Man.


Good Luck.

Is this what you mean about it (the fan?) not running below freezing?

someone showed me the installation instruction manual here http://iompics.com/downloads/Heat P...e/Install Instructions 25HCC5/25hcb-c-5si.pdf
and I saw this:

Defrost
The defrost control is a time/temperature control which has field
selectable settings of 30, 60, 90, or 120 minutes, factory set to 90
minutes. These settings represent the amount of time that must pass
after closure of the defrost thermostat before the defrost sequence
begins.
The defrost thermostat senses coil temperature throughout the
heating cycle. When the coil temperature reaches the defrost
thermostat setting of approximately 32_F (0_C), it will close,
which energizes the DFT terminal and begins the defrost timing
sequence. When the DFT has been energized for the selected time,
the defrost cycle begins. Defrost cycle is terminated when defrost
thermostat opens, or automatically after 10 minutes.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Yep Yep.

You may want to try after it gets a bit warmer.

It could be going into defrost.

Is your electrical strip heating working ?

If so it may be best and cheaper to use that, when below 32F.


Good Luck.
 

khalsa

New Member
Messages
7
Reaction score
0
Points
1
Location
MD
Yep Yep.

You may want to try after it gets a bit warmer.

It could be going into defrost.

Is your electrical strip heating working ?

If so it may be best and cheaper to use that, when below 32F.


Good Luck.

Thanks.
It is working fine. If it is going into defrost, I think it stays there-- but I can't hear anything. I'll check it out in a few days once the temps reach over freezing. I will keep you posted.
 
Last edited:

Nukeman

Nuclear Engineer
Messages
707
Reaction score
1
Points
18
Location
VA
My guess is it is something else. Even if it goes into defrost, the fan (outdoor) will stop, but you will still hear the compressor run. The defrost will terminate when either the coils warm up enough or if it has been in defrost for 10 minutes. At that point, it will go back into normal operation.

With the defrost timer set to 90 minutes, the coil must be freezing for 90 minutes before the defrost cycle begins. So, it goes like this (when in heat mode):

1. coil temperature sensed below 32F
2. defrost thermostat closes and starts timer
3. if the defrost thermostat remains closed until timer expires (90 minutes w/ factory settings), the defrost cycle will start
4. when defrost is complete (or if 10 minutes has past) it goes back into normal operation and the steps repeat

If ambient temperature are low (below 32F), the coils will be even colder (how a heat pump works), so you will get 1 defrost cycle every ~90 minutes with those settings.

I would get a tech to look at it (or we can dig more into it, if you are comfortable). It could be something related to the run capacitor or it may be locking itself out to protect the compressor (low pressure, etc.).

For the crankcase heater, it only specifies one being needed if the lineset is 80' or longer (or if outdoor unit 20' lower than indoor unit). My unit is a different brand and does not use a crankcase heater.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
I agree with Nukeman, that was a great explanation of how the system Should work.

There are many things that can hose the sequence of events.

If it is a bad Capacitor and it is very cold, sometimes heating them up will help get the electrolytic in them work better and can increase the capacitance. A hair dryer can do that, just for a test. It is best just to measure them, and a good technician will have the proper tools.

If it is in warranty you are better off to call the man, but a service call for labor can get expensive, even if parts are under warranty.

As Nukeman pointed out you could have a refrigerant leak.


Good Luck.
 

airtrackinc

New Member
Messages
1
Reaction score
0
Points
0
Location
Ontario
Website
www.airtrackhvac.com
Start and run capacitors are commonly replaced when the system is not starting or running correctly.

If you suspect the start or run capacitor to be faulty, disconnect all external wiring from the start capacitor. Ensure power is off and proper safety precautions are taken. Ensure that there is no charge in the start capacitor. This can be accomplished by using an touching both terminals with the same metal object at the same time (some like to use a screwdriver with a an insulated handle). Make sure that your hands are insulated from the metal so that you don't get a shock!

Using an ohmmeter, test both terminals. If the reading is infinite, the capacitor is good. If not, the capacitor should be replaced.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Using an ohmmeter, test both terminals. If the reading is infinite, the capacitor is good. If not, the capacitor should be replaced.

If the capacitor is open, that test will tell you nothing.

You should reverse meter leads and the reading will be close to a short, for a very brief period, because you are reversing polarity, and then go to infinite if the cap is charging and is not shorted.

I think you just missed a step, but the precautions given are good.
 

khalsa

New Member
Messages
7
Reaction score
0
Points
1
Location
MD
Money has been tight, so I haven't done anything about my heat pump. I would like to update this a bit and see if anyone can pinpoint the issue a bit. When I run the AC, the fan keeps spinning on the heat pump (it doesn't shut off after a couple seconds like it does when the heat is running). The air handler inside the house also gives of a loud high pitched whistle while the AC is on.

Any thoughts?
 
Last edited:

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Bad motor bearing maybe.

Does your t-stat ever get satisfied ?
 

khalsa

New Member
Messages
7
Reaction score
0
Points
1
Location
MD
satisfied? not sure how i can check it. the heat will run via the furnace (air handler or whatever is in the house) but it isn't very effective and will be in emergency heat.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
satisfied? not sure how i can check it. the heat will run via the furnace (air handler or whatever is in the house) but it isn't very effective and will be in emergency heat.


Does it get to the temp that you set it to, is what I meant.

Does the unit work in air conditioning mode ?
 