Page 1 of 2 12 LastLast
Results 1 to 15 of 27
Thread: How much work is the heat load calc
    DIY Member Soapm's Avatar
    Dec 2013
    Aurora, CO
    Default How much work is the heat load calc
    We've brought in a few companies to get estimates on using split systems to heat our sanctuaries and so far none has done any calculations. They look at the two furnaces currently heating the sanctuary and start telling us what products they have that can match that capacity.
    I want to make sure we don't buy more than what's needed since that would be a giant waste and from what a read, less effective.
    DIY Senior Member houptee's Avatar
    Aug 2008
    Monmouth County, NJ
    There is free software out there to do it yourself if you google free heat loss calculator.
    Here is one for android and apple
    http://www.slantfin.com/homeowners-page/ipadapp.html
    Here is a web based one
    http://www.builditsolar.com/Referenc...s/HeatLoss.htm
    In the trades Dana's Avatar
    Jan 2009
    The SlantFin tool is an I=B=R spreadsheet type, with GENEROUS U-factors on the construction type. In a residential app it will usually overestimate the load by about 25-35%.
    For sanctuary buildings that are often unoccupied with deep temperature setbacks it's usually a good idea to oversize by 50-100% to shorten the temperature recovery ramp to something reasonable during the coldest weather. If it's to be kept at temp or set back to only ~5F below the normal temp you can size it dead-on (or even 10% under) the Slant-Fin calculated heat load at the 99% outside design temp and never be cold.
    If the heat pumps have resistance-electric coils as auxilliary heating and you're using deep setback strategies for more than 12 hours/day, size the heat pump output (before the coils kick on) for the heat load at the mean January temperture, or between the January mean daily low and mean temp. It'll always run the resistance heaters for part of the recovery ramp, but once it's up to temp the heat pump carries the load, as well as nearly 100% of the load at the deep setback temp.
    Jul 2009
    North Vancouver, BC
    Quote Originally Posted by Soapm View Post
    When I bought my Knight Boiler the supplier did the Heat Calc for $75.00 - with engineering documents and a stamp. This fee was deducted from the price of the unit at purchase time.
    No brainer....
    Jan 2009
    In commercial & industrial spaces the heat load calc is just the starting point- usage patterns actually matter, and differ quite a bit from residential applicaitons. Air source heat pumps add even more complexity to the mix (extended temperature output tables, determining the crossover points for kicking on the auxilliary heating strips, etc.) Sizing a heat pump is never a fully straightforward thing the way it is with heating boilers, even for residential applications.
    A $75 heat load calc is often worth less than what's charged, (even in residential applications) since that sum doesn't come close to covering the amount of time it takes to actually do it right in a fully Manual-J compliant manner (or even I=B=R).
    Nov 2010
    Maine
    The easiest thing to do is look at the current fuel usage and K factor which is probably what the two contractors both have done. If I can get an accurate use and K there's no way I'm spending a few hours to do a manual J, especially on a commercial, non-full occupied use structure.
    Jan 2009
    There's a reason why Manual-J only really applies to residential apps, eh? ;-)
    I would think a heat load calculation is the 1st thing. Any heating or cooling guy worth having would do that before he recommended a unit. Typically the old system would have been over sized because bigger is better right? Well from what I have read that is not the case in the heating and cooling biz. Correctly sized system will save you money and work good. Over sized will cost extra $$$ and may not work good. Undersized and your cold (winter) or hot (summer)insist on a heat load calculation or move on to the next guy. For the money it costs for a new system maybe you can pay for one yourself.
    Politicians are like diapers. You need to change them often……for the same reason.
    Nov 2010
    Maine
    Because this structure is a church, 90% of their heating and cooling loads are for one day a week. I would believe that they either have a set back thermostat or someone cranks the heat back during the rest of the week (cooling in the summer) So we're really not all that interested in maximum efficiency although we don't want to grossly oversize the equipment either. What they need is a balance between operating cost and being able to either recover heat fast or cool the place down fast. Sized for daily occupancy both the heating and cooling systems would be sized for the daily, occupied load without deep set backs but that requires running the systems 24 hrs a day at temperature. Here we need reasonable operating costs but we really need rapid recovery. If the system is oversized its really only going to run at max temperature for a few hours a week. I personally have screwed myself in this same scenario. In my zeal to prove that a local church's equipment was grossly oversized, when they needed a new furnace I did the heat loss and naturally I was proved correct so I sold them two Ruud 90++ condensing furnaces to replace the single huge Lennox beast. All things being the same, they set the thermostats back to 50 during the week and lo and behold, in order to get the church up to 70 for Sunday sermon, they had to crank the thermostat back up on Thursday. Not happy customers but.........the lord forgivith and so did they after I added another furnace and A coil to the mechanical room at...... Cost (: No good deed goeth unpunished
    Dec 2013
    Aurora, CO
    The guy that came out today took the time to explain a lot of this to me. I appreciated his education which will make a huge difference when I go before the congregation. He said the building is usually empty and comfort isn't as important to an empty building. However, Sunday comes, you got heavy traffic with the doors opening and closing them a room full of 98.6 degree's people. Add to that the fact that the sanctuary is open to the rest of the building which is on a separate boiler so that makes makes exact calcs a moving target.
    Then he suggested we stay with the existing furnaces since heat pumps are really good to 30 degree's outside temp and said the electric that kicks in at 30 degree's is more expensive than running the old furnaces. He suggested we use the splits for summer cooling only and not get the heat pump option. Does that sound about right?
    Then he said a big unit designed for multiple heads with one head will be about $4K and about $1K per additional head. Is that about right? This is no heat, just cooling...
    He's kind of talking himself out of a job because as soon as he left we got a loud squeal from one of the furnaces. The bearings went out on one of the blower cages and set us back $275.00... The temp today was -2 degree's so what else could we do but go with the first quote...??? I don't think he get's it, we want to replace those 1983 furnaces AND get cooling if we can work it into the solution...
    Nov 2010
    Maine
    From a reliability stand point it might be a good idea to replace the furnaces but again, even though they are 30 years old, they really don't get a whole lot of use so yes, blower bearings were an issue and someone that knows their stuff should go through them and repair or replace worn parts but unless the heat exchangers are cracked those furnaces are not a whole lot worse or different efficiency wise than brand new ones of the same type would be. I do like the idea of leaving them and going with mini-splits for the AC though. Unless the church plans on running them full time though, like the furnace they will need to be oversized to rapidly cool the area's just prior to use.
    Jan 2009
    There are plenty of heat pumps that have significant output and decent efficiency at temps down to +5F (and ductless heat pumps good to -15F). The outdoor temperature at which the resistance heaters kick in is NOT fixed at 30F, it's a design/sizing decision.
    Your description of the heat pumps said "split systems" which refers to ducted split units with air handlers, but when you talk about " ...big unit designed for multiple heads...) it sounds like a reference to ductless mini-splits. Which is it?
    If the latter, look into the just upgraded/released Mitsubishi M-series, with many models good down to -13F and comes in a wide variety of multi-split options, if that's really called for. eg. The MXZ-8B48NA is a 4-ton (nominal cooling) unit that can handle up to 8 heads or cassettes of mixed sizes & types. The PUZ-HA36NHA is a pretty-good 3-tonner, good for 38,000BTU/hr @ +5F, and about 30K @ -13F.
    Rooms that are doored-off from the main sanctuary don't all necessarily need a separate head- if it doesn't have design load of at least 5000BTU/hr it arguably should NOT get it's own. Mini-ducted cassettes can split output between adjacent pairs of rooms. Some rooms may need to be heated with something else if the installation is too awkward or the load is too small. (Radiant cove heaters are a good option for temperature balancing rooms not served by the ductless system.)
    Replacing the antiques with condensing gas furnaces would be cheaper up front and may even be cheaper to operate, but don't provide air conditioning, and may not be worth the expense if the existing ~78% efficiency burners have any life left in them.
    If you install ductless units for cooling it's worth the upcharge for units that both heat & cool, even if the heat output doesn't fully meet the load. During the shoulder seasons when the temps are in the 40s, heating with ductless systems can be even more efficient than with ground source heat pumps, and cheaper than heating with condensing gas. As an optimizing control strategy setting the thermostats for the gas furnaces several degrees below that of the ductless lets the ductless carry the load until until it just plain can't.
    Without any information on the sizing of the existing gas-burners, fuel use against heating degree day, or usage pattern information it's hard to get particular about what could/could-not work. Typical heating + cooling single head high-efficiency ductless units that operate in cold climates runs about $3-3.5K/ton, all-in turnkey price. (The Fujitsu XLTH series and the Mitsubishi "FH" series are good to look at for up to 1.5 ton single-head units.) A 3 ton multi might run $5-6K for the compressor unit, $1-2K per cassette or head (depending on exactly which cassettes/heads are used.)
    Dec 2013
    Aurora, CO
    Fujitsu was out today and recommended four of these http://www.fujitsugeneral.com/wallmountedRLF.htm
    The sanctuary is 63 feet by 43 feet with a sloped ceiling that peaks at 20 feet. It holds 225 bodies though it's been a long time since it's been full. He said we'd be comfortable down to about 20 degrees with two of these mounted in the front and two mounted in the rear, all four up high. He did say the heat pumps would work down to 0 degrees so I guess the 20 degrees is when the effectiveness begins to taper off???
    Currently we have two natural gas Lennox G8, the highest capacity they came. I know the guy said over 200K but not sure what it was but he did say it was the biggest for that model. We'll keep these but they'll only be needed on extremely cold days. My zip is 80010.
    Any experience or reviews on this Fujitsu model? Does this sound like a viable solution?
    Last edited by Soapm; 02-25-2014 at 04:48 PM. Reason: Changed the link from brochere to product page
    Jan 2009
    Your link isn't working for me- how about just the model numbers?
    The output capacity starts falling off below 60F, but it's not entirely linear, and the question becomes how much capacity does it have relative to your heat load at the 99% outside design temperature. Different mini-splits have different output characteristics as the temperatures fall off, but many are still delivering about 2:1 efficiency at full speed at 0F and below. Whether it has the capacity to cover full heat load at 0F is a separate question, which requires some sort of heat loss analysis. Some heat pumps have no specified output rating at 0F, even though they don't stop working, others are specified down to -15F or below.
    Heat load is not a function of the square feet of conditioned space- it's all about the exterior surface areas of different construction or material types, and the temperature difference between the indoors & outdoors. The 99% temperature bin for your zip code is about 0F, so if the system is sized EXACTLY for the full load at for 0F will means you won't lose ground except during the pre-dawn hours of the coldest nights of the decade. Turning on the lights and putting even 30 live bodies in the pews takes quite a bit off the the load that the heat pump has to carry.
    If you want to run a quick & dirty I=B=R type load calc on it we'll need to know the total amount of wall area (with construction type and R-values), window area & type, roof area and type, as well as the total door area & type so we can come up with reasonable U-factors.
    A typical single-pane window with no-storms loses about 1 BTU/ per hour per square-foot per degree difference, so with an interior temp of 70F and an outdoor temp of 0F you have a 70F difference for 70F x U1= 70 BTU/hr per square foot of window. Add clear storm windows and it's half that.
    Solid 2" doors run about 0.5 BTU/hr-degree-foot.
    A 2x4 studwall with fiberglass loses about 0.1 BTU/hr-degree-foot. A 2x6 studwall with fiberglass loses about 0.077 BTU/hr-degree-foot. A brick-veneered CMU wall with no insulation runs about 0.3-0.5 BTU/hr-degree-foot, but with an inch of foam in the cavity between brick & CMU it's in the ~0.14 range.
    A 2x6 t&g cathedral ceiling with no insulation with composite shingles and no snow load runs about 0.6 BTU/hr-degree-foot. With 2" of exterior foam under the shingles that falls to about 0.1.
    Full basement, or slab-on-grade?
    Only count the walls where the exterior is the great outdoors, not partition walls to other conditioned spaces.
    Dec 2013
    Aurora, CO
    the model number is Fujitsu 30RLX.
  1. Heat load calc help
    By Handymaner in forum Boiler Forum
    Last Post: 08-27-2012, 01:16 AM
  2. Using Cable Electric Heat as a primary heat source in your bathroom (Heat Loss Calc)
    By johnfrwhipple in forum Shower & bathtub Forum & Blog
    Last Post: 08-25-2012, 05:02 PM
  3. Heat Loss Calc. Help
    By molo in forum HVAC Heating & Cooling
    Last Post: 12-06-2011, 10:35 AM
  4. Replies: 2
    Last Post: 03-23-2011, 06:34 AM
  5. online heat loss calc???
    By Gnfanatic in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Last Post: 07-22-2010, 09:32 PM