Thread: Looking for options to terminate sump pump line

  1. #1
    DIY Junior Member word2yamutha's Avatar
    Join Date
    Sep 2013
    Location
    Missouri
    Posts
    9

    Default Looking for options to terminate sump pump line

    I currently have 1.5 " pvc from the sump pump to outside my house. I want to bury my lines, but afraid they will freeze. I plan on going from 1.5" to 4" PVC with a 2" air gap in between them. My main problem is I'm not sure where to terminate the line. I live in a corner lot so my options are limited. I thought about running a 4" line underground the using a pop up emitter to the street. Will the pump have enough pressure to use the pop up emitter?

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,147

    Default

    The pump pressure will have no effect on the pop-up because the only pressure beyond the air gap is head pressure from the gradient of the pipe. If you cannot achieve at least 1/8" per foot of gradient you will be likely to have a problem with ice. If the pipe is a couple of feet below grade or has snow cover, it is less likely to freeze.

  3. #3
    DIY Senior Member Reach4's Avatar
    Join Date
    Sep 2013
    Location
    IL
    Posts
    1,254

    Default

    I interpreted that he would use the 4 inch as a sleeve hoping that the layer of air between the top of the 1-1/2 inch and the 4 inch pipes would serve as insulation.

    The pop-up back pressure won't be a problem unless it is iced over.

  4. #4
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,147

    Default

    That might be what he meant, but it would be a mistake if he did it. The piping must have an air gap and must be able to gravity drain.

  5. #5
    DIY Senior Member Reach4's Avatar
    Join Date
    Sep 2013
    Location
    IL
    Posts
    1,254

    Default

    WHAT???

    You are saying that a line from a sump pump to a pop-up in the yard needs an air gap?

  6. #6
    DIY Junior Member word2yamutha's Avatar
    Join Date
    Sep 2013
    Location
    Missouri
    Posts
    9

    Default

    Quote Originally Posted by cacher_chick View Post
    That might be what he meant, but it would be a mistake if he did it. The piping must have an air gap and must be able to gravity drain.
    I was going to do this. Id rater have an airgap just in case a pipe freezes and has a way to exit. Id rather not flood my basement.

Similar Threads

  1. is this a right way to terminate a drain line?
    By diyfun in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 03-25-2013, 07:42 AM
  2. Ventless Pump: 1) Any good? 2) How to terminate?
    By bucky in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 08-09-2011, 07:04 AM
  3. Basement bathroom plumbing options (pump up to septic line)
    By mrmichaeljmoore in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 11-04-2009, 08:01 AM
  4. Burying line for sump pump
    By cacher_chick in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 04-12-2008, 06:52 PM
  5. Sump Pump Line reducing question
    By average_male in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 09-05-2007, 09:34 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •