Thread: water heater vent location

  1. #1
    DIY Junior Member Rocco1's Avatar
    Join Date
    Feb 2014
    Location
    NJ
    Posts
    3

    Default water heater vent location

    I need to relocate the vent termination for my BradfordWhite gas HW heater. Model M1TW50S6FBN, 50gal. 40,000 BTU input.

    The current location is now posing a trip hazard for my deck stairs in addition to being below the snow clearance height. There are several concerns that I need to consider with the new placement.

    NFGC - Code states:
    12.9.2 A mechanical draft venting system of other than direct-vent type shall terminate at least 4 feet below, 4 feet horizontally from, or 1 foot above any door, operable window, or gravity air inlet into any building.
    12.9.3 The vent terminal of a direct-vent appliance with an input of 10,000 Btu/hr or less shall be located at least 6 inches from any air opening into a building, and such an appliance with an input over 10,000 Btu/hr but not over 50,000 Btu/hr shall be installed with a 9 inch vent termination clearance, and an appliance with an input over 50,000 Btu/hr shall be at least a 12 inches vent termination clearance.

    explanation of the code: Subsection 12.9.3 permits the vent terminals of direct vent appliances to be located much closer to air inlets than is provided for with mechanical draft equipment. There is often a mis application of rules for mechanical draft to direct vent equipment. The vent gases from direct vent equipment disperse rapidly upon leaving the vent terminal, even when the terminal is located under an open window.

    installation instructions/code also state that the exhaust needs to be 4' to the side of a combustion air inlet to any other appliance. also, 24" vertically to an unventilated sofit

    What I cannot determine what my unit is classified as. It's listed as a "power vented gas water heater" but is it a "mechanical draft venting system' or a "direct vent".

    I also have two concerns. 1) how far horizontally does this need to from the input for my 95% furnace (the furnace is a dual pipe configuration - intake and exhaust are both piped to the outside) and 2) can this unit exhaust 24" below an openable window. The window is a bump out 24" above the proposed vent termination.

    thanks

  2. #2
    DIY Junior Member Rocco1's Avatar
    Join Date
    Feb 2014
    Location
    NJ
    Posts
    3

    Default

    Name:  IMG_1558.jpg
Views: 98
Size:  49.1 KB proposed location is to the right of the vent termination for furnace

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    The products of combustion can pose a problem for a direct vented system, so you would not want the WH vent to be too close to the furnace's. Personally, whether it is allowed or not, I would not want those exhausts beneath a window.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,714

    Default

    Quote Originally Posted by jadnashua View Post
    The products of combustion can pose a problem for a direct vented system, so you would not want the WH vent to be too close to the furnace's. Personally, whether it is allowed or not, I would not want those exhausts beneath a window.
    Or even under an overhanging cantilevered floor, since that is a notorious location for infiltration leakage into houses. (If you haven't already, air-seal and insulate those joist bays where they cross over the foundation, and the foundation sill too. Use a blower door or large window fans and to both pressurize & depressurize the house while air sealing, tracing the leak points with a smoke pencil to make sure you nail all of 'em.)

  5. #5
    DIY Junior Member Rocco1's Avatar
    Join Date
    Feb 2014
    Location
    NJ
    Posts
    3

    Default

    Quote Originally Posted by Dana View Post
    Or even under an overhanging cantilevered floor, since that is a notorious location for infiltration leakage into houses. (If you haven't already, air-seal and insulate those joist bays where they cross over the foundation, and the foundation sill too. Use a blower door or large window fans and to both pressurize & depressurize the house while air sealing, tracing the leak points with a smoke pencil to make sure you nail all of 'em.)
    Thanks for the tips but I really just need to know if it is permissible to relocate the vent to his proposed location 4ft to the right of the furnace input/output location. The exhaust for the furnace passed inspection at its current location so I'm assuming the 24" under the window is allowable. (I know, common sense dictates that the window would be closed during the time when the furnace is running but I can't imagine that matters when it comes to code- it's either allowed or it's not) I'm really not going to get into pressurizing the whole house to check for a leak of air.

  6. #6
    DIY Member Soapm's Avatar
    Join Date
    Dec 2013
    Location
    Aurora, CO
    Posts
    47

    Default

    Could just make that the mother in law room and be done with it...

    J/k... I'm pretty lucky, I actually get along well with my in laws.

  7. #7
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,714

    Default

    Review the relevant sections of chapter 12, beginning on p.52 (p.88 in PDF pagination) particularly section 12.9.3 and FIGUREA.12.9 on p.119 (p.125 in PDF pagination.)

    Given that power vented burners depressurize the house WHILE they are running, simply not bothering to air seal and test the integrity of the air seal at that critical location seems imprudent. The typical measured leakage at foundation sills is well in excess of windows, even LEAKY windows. When a gas burner is operating properly the health risks of leakage at that location are pretty low, but over the lifecycle of the unit virtually all gas burners will misfunction at some point.

  8. #8
    Master Plumber Caduceus's Avatar
    Join Date
    Oct 2013
    Location
    Pittsburgh, PA
    Posts
    99

    Default

    Okay, I'll answer your question. Your power vented water heater is a mechanically drafted vent system.

  9. #9
    Master Plumber Caduceus's Avatar
    Join Date
    Oct 2013
    Location
    Pittsburgh, PA
    Posts
    99

    Default

    Sheesh. Wasn't like he was asking how to build a freakin' space shuttle.

Similar Threads

  1. water heater location
    By flowdw in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 09-24-2013, 12:51 PM
  2. Water Heater Vent Location? Am I an idiot?
    By Murphy625 in forum Water Heater Forum, Tanks
    Replies: 5
    Last Post: 08-19-2013, 01:01 PM
  3. location of water heater
    By jcds in forum Canadian Plumbing Code Questions
    Replies: 2
    Last Post: 11-11-2012, 11:41 AM
  4. What is needed for new water heater in new location?
    By alwaysfine in forum Water Heater Forum, Tanks
    Replies: 4
    Last Post: 12-11-2010, 06:49 AM
  5. Water Heater Location?
    By Michael McCann in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 10-26-2006, 08:39 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •