    Help! Planning a main bath remodel for a 1920's house with a single pipe steam heat system. Bath has a large radiator in it that we would like to remove. What options are available that would allow us to use the available steam, without the large radiator taking up space?

  2. #2
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    All good solutions are going to start with a room-by-room heat load calculation, which will determine the zone balance and the minimum size steam radiator that will work. If part of the remodel is to air-seal and insulate the exterior walls and install high performance windows you may be able to skip the radiator entirely. (You may also be able to run it as it's own zone using pumped hot water radiation rather than the steam, but that would run counter to your stated desire to use the available steam plumbing.)

    Cast iron baseboard often works well in bathrooms- just be sure to not install baseboard radiation directly behind/under the toilet. It comes in a number of different heights, with different BTU/linear foot or equivalent square feet direct-radition per foot ratings, and is period-appropriate if you're trying to preserve the 1920s craftsman-look:



    Small thin profile wall-cut-in type radiators like the classic Sunrad, or Burnham Radiant can also work well, if that's a better fit. They're about 5" deep, 20" tall, and come in any number of widths:

    SunRad

    SunRad




    Radiant

    Radiant

    Be sure to insulate VERY well if putting it on an exterior wall. (Thinning out the framing to 2.5", compressing in a snug-fitting R11 batt into that 2.5" depth, then adding 1-1.5" of foil faced rigid polyiso on the interior side as a thermal break on the studs keeps it from sending 15% of the heat outdoors.)

  3. #3
    DIY Senior Member jim mills's Avatar
    Join Date
    Jan 2014
    Location
    nebraska
    Posts
    137

    Default

    I have seen a toe kick heater & was hoping that something like that would work, but I found out they are forced hot water, not steam. I hear you can run forced hot water off a boiler using a heat exchanger, but way too complicated & costly for this application. Actually, that baseboard heater in your first picture might just be the perfect solution. Is ther an issue having it too close to the toilet though?

  4. #4
    DIY Senior Member houptee's Avatar
    Join Date
    Aug 2008
    Location
    Monmouth County, NJ
    Posts
    177

    Default

    Too bad your not near NJ i have a bunch of cast iron rads and baseboard sections I took out after Sandy flooded my house. They will probably end up going to the scrap yard since nobody seems to want them. They have been outside so they rusted but could be sandblasted and repainted.
    If you look on craigslist you might find some radiators near you for sale cheap.

  5. #5
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,964
    Blog Entries
    5

    Default http://www.oldcastironradiators.com

    I bought mine all brand new from this place.

    http://www.oldcastironradiators.com

    They have loads of sizes and options for you to try out. They ship anywhere I'm told. One in three rads in North America originally come from this family owned company. The moulds are the same today as they where 100 plus years ago.






    I have the 4 column #29 in my home
    Last edited by johnfrwhipple; 02-05-2014 at 06:44 AM.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  6. #6
    DIY Senior Member jim mills's Avatar
    Join Date
    Jan 2014
    Location
    nebraska
    Posts
    137

    Default

    Thanks John. I'll check them out. The problem is the existing radiator sits right next to the tub, taking up about 3' of wall space. Then sits a pedestal sink, then the toilet. They want to remove the radiator & put in a 60" vanity. Makes sense, six kids & a pedestal sink don't cut it...
    Name:  bath.jpg
Views: 101
Size:  17.3 KB

  7. #7
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,964
    Blog Entries
    5

    Default

    Maybe you can design a bench of sorts and cover the new Rad. Somewhere to put some baskets and some crap for the family.

    ???

    Make sure you clean the connection threads well when you hook up the new rad. I had a few poor connections I think because I didn't do a good job of cleaning these dirty threads. Ran the system in my garage for a few weeks to monitor the rads before hooking a few up. Love the heat and the look of them.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  8. #8
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,642

    Default

    Quote Originally Posted by johnfrwhipple View Post
    I bought mine all brand new from this place.

    http://www.oldcastironradiators.com

    They have loads of sizes and options for you to try out. They ship anywhere I'm told. One in three rads in North America originally come from this family owned company. The moulds are the same today as they where 100 plus years ago.


    Just looking at them make me miss my grandparents.

    This is more my speed.

    Name:  TRD40615T.jpg
Views: 98
Size:  3.5 KB
    http://www.delonghi.com/en-US/produc...diant-heaters/
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  9. #9
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    The issues with putting steam baseboard radiation directly under/behind toilets are twofold:


    1: The toilet can heat up to a very uncomfortable temp during cold weather (or during recovery from setbacks) when the duty cycles on the heating max out.

    2: The overly-warm toilet causes the seal to the drain to fail (and the traditional wax seals can melt entirely!)

    Even though it's traditional to put the radiators under windows (a practice begun back in the day of leaky single-panes, that collected copious frost/condensation otherwise), it looks like you have sufficient wall length between the door and the right side wall to put cast iron baseboard opposite the toilet & sink, maybe even turning the corner, stopping before it's even with the toilet. Whether that's easy or difficult to implement the way the current steam plumbing is currently routed under the floor isn't obvious. The two biggest vendors of c.i. baseboard are Burnham ( the product line is called "BaseRay"), and Weil McLain (called "Snug".) The ~8"-9" tall versions have comparable output-per-foot to 2" fin-tube type baseboard, but since a large fraction of the output is radiated rather than convected (almost all fin-tube output is convected air) it's noticably more comfortable.

    Heat loads of bathrooms are pretty low- the size of the radiation needs to be reasonaly balanced with the radiator sizes relative to their room loads on the rest of the system though so that you neither overheat or under heat the bathroom relative to the rest of the house. If the existing radiator is sized with reasonable temperature balance, you can measure it up to determine it's "Effective Direct Radiation" (EDR) size which can be applied to the EDR of the new radiator or baseboard. It doesn't have to be exactly the same EDR as the original radiator but keeping the new radiator neither more than 1.5x nor less than 0.5x would be prudent, if it's working OK now.

  10. #10
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,964
    Blog Entries
    5

    Default

    Jim if you work out the heat calc for the room you can call the company I mentioned and they will tell you what unit you need. My kitchen is huge with 3 5'x3' windows on the South wall

    1 single lite french door 1 5'x3' window and 1 3'x2' window on the West Wall and I have only two rads.

    Both 4 fin. One 20 stacks one 8 stacks.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  11. #11
    DIY Senior Member jim mills's Avatar
    Join Date
    Jan 2014
    Location
    nebraska
    Posts
    137

    Default

    Thanks Dana. The reason I asked about a radiator behind a toilet is that your first picture shows a radiator beside a toilet. I couldn't understand why this would work, but not behind. I will be turning this over to the boiler man soon, but want to be as informed as I can be before I do.

  12. #12
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    Quote Originally Posted by jim mills View Post
    Thanks Dana. The reason I asked about a radiator behind a toilet is that your first picture shows a radiator beside a toilet. I couldn't understand why this would work, but not behind. I will be turning this over to the boiler man soon, but want to be as informed as I can be before I do.
    When the radiator is behind the toilet the convecting air column is impeded and more of the heat ends up in the toilet, (including the water in the tank). A foot or so of clearance (just a WAG) to the side should be sufficient space that the toilet itself can convection-cool enough from it's absorbed radiated heat to keep it from getting too far out of hand. Tucked in there as in the picture it still might not be the most-comfortable under high heating duty-cycle conditions, but it probably won't melt the wax seal.

    FWIW: In my own home in a tiny upstairs bathroom I have a section of Weil McLain Snug on the wall behind the toilet that extends ~1/3 of the way under the tank, but not behind the bowl. But it's a pumped hot water system @ 130F max water temp, not 220F steam. Even that bit warms the toilet enough to be noticed by the user, but not enough to lead to discomfort. I haven't measured the actual toilet temp, but it's probably hitting around 80-85F. Even 25F warmer would be uncomfortable to sit on.
    Last edited by Dana; 02-06-2014 at 12:32 PM.

  13. #13
    DIY Junior Member emmet_97's Avatar
    Join Date
    Mar 2014
    Location
    NJ
    Posts
    1

    Default I am in NJ and looking for replacement sunrads. If you can help it is appreciated

    Quote Originally Posted by houptee View Post
    Too bad your not near NJ i have a bunch of cast iron rads and baseboard sections I took out after Sandy flooded my house. They will probably end up going to the scrap yard since nobody seems to want them. They have been outside so they rusted but could be sandblasted and repainted.
    If you look on craigslist you might find some radiators near you for sale cheap.
    I am in NJ and looking for replacement sunrads. If you can help it is appreciated

  14. #14
    DIY Senior Member CanOfWorms's Avatar
    Join Date
    Feb 2013
    Location
    New Jersey
    Posts
    157

    Default

    Try this. It looks great works great and is something you can brag about.
    If you use 3 x 3' sections you just added 12' of baseboard
    Name:  radiator loop.png
Views: 12
Size:  5.9 KB

  15. #15
    Master Plumber nhmaster3015's Avatar
    Join Date
    Jul 2008
    Location
    The granite state
    Posts
    102

    Default

    You can pull a hot water loop off the bottom of the steam boiler. You need a circulator and an aquastat.
    Don't believe everything you hear, go find out for yourself.

Similar Threads

  1. 1/2 to3/4 bath remodel
    By jdavis in forum Remodel Forum & Blog
    Replies: 1
    Last Post: 04-10-2011, 03:28 PM
  2. Bath remodel
    By strikebd in forum Remodel Forum & Blog
    Replies: 2
    Last Post: 04-14-2008, 12:10 PM
  3. Bath Remodel
    By tchad04 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 02-13-2008, 12:47 PM
  4. Bath Remodel
    By bagjeff in forum Remodel Forum & Blog
    Replies: 4
    Last Post: 01-22-2007, 09:07 AM
  5. Bath Remodel
    By JCR in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 11-19-2006, 07:45 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •